I've encountered an install of 6" duct directly connected to the outside through the rim joist and covered by a simple mess screen on the end.  The other end has been placed next to the gas furnace as make-up air.  The cold air just pours in whether the furnace is active or not.  There is a clear need for make-up air as the CAZ is very small and the DHW and furnace are next within a couple of feet of each other.  Any advice on a simple mechanical option to better regulate this situation.  (The DHW is natural draft and the furnace is power-assist.  They are commonly vented.)   

Views: 354

Reply to This

Replies to This Discussion

Let it be known common venting of power draft and natural draft appliances is against code in many jurisdictions. Are the DWH and Furnace in conditioned or unconditioned space?

The units are in a conditioned laundry area, 16'X11'X7.5'  The DHW is 36K btu & furnace 45K btu. (Dryer is electric.)

Hi Jerry, your classic can of worms.

Each of us must decide where we will draw the line, that line where we can be blamed for making conditions worse and this is one.  Any improvements on air sealing could affect that CAZ, therefore, IMO, I advise the problems need to be fixed FIRST, before I will continue with an audit.  I usually catch these with a pre-audit visit, but that's my routine.

Here is some of what you face and I'm not a pro on HVAC as Maine prohibits auditors from doing anything beyond the specified CAZ test. 

1.  Venting as Bob mentioned needs to meet code.

2.  Replacement air also needs to meet code, such as vent area, high and low vents, and outside clearance.  A 6" duct is way too small.

3.  Any mechanical solutions need to be approved for that use, no shoe strings and cloths pins.

A common recommendation is a cold air trap with a bucket or a 180° turn in the incoming duct.  The short explanation is, they don't do as advertised and neither would bring the venting up to code.

Most burner units, and you have two, have combustion air kits that can draw air directly from the outside.  There are also powered dampers which open and close as needed and prevent the burner from coming on if they fail.  Whether either of these could be used to solve the problem and meet the codes would need to be determined.

Again, this is my opinion and perhaps others will chime in with some code requirements, beyond my scope.

Bud

Picture of uncontrolled make-up air duct next to furnace.

 

Attachments:

Glad they used insulated duct for the fresh air intake ;)

Have you considered sectioning off the water heater and furnace from the rest of the laundry area? Make the that unconditioned space. How about a vent between the laundry area and the rest of the house effectively increasing the size of the laundry room and eliminating the need for make up air?

Be sure to check local codes before making a final choice. As Bud said this may be a HVAC contractors issue, although I probably wouldn't call the one that stuck in the 6" flex for fresh air...

RSS

Featured Forum Discussions

What's the Most Profitable HVAC Job for Your Company?

Started by Wayne Melancon in HVAC. Last reply by Eric Kjelshus 3 hours ago. 2 Replies

Lighting replacement - 300 watt LED flood light

Started by Mary Sinkler in General Forum. Last reply by Jan E. Graveamker 8 hours ago. 4 Replies

Glass Block Windows

Started by Ken Kalke in Best Practices. Last reply by Sean Lintow Sr on Saturday. 1 Reply

EZ Green Home is Hiring!

Started by Chloe Chapman in General Forum Jan 5. 0 Replies

Videos

  • Add Videos
  • View All

Latest Activity

Eric Kjelshus replied to Wayne Melancon's discussion What's the Most Profitable HVAC Job for Your Company?
"What is your "Key Performance Indicator" dollar per hour? gross dollar per man day? % of…"
3 hours ago
Jan E. Graveamker replied to Mary Sinkler's discussion Lighting replacement - 300 watt LED flood light
"Hi Mary, What is the purpose of lighting the backyard ?  Sense of safety, night time…"
8 hours ago
Chris Laumer-Giddens liked Chris Laumer-Giddens's blog post Rock Wool Insulation for Floor of High Performance Tiny House
9 hours ago
Joe Davis liked Wayne Melancon's discussion What's the Most Profitable HVAC Job for Your Company?
12 hours ago
Joe Davis replied to Mary Sinkler's discussion Lighting replacement - 300 watt LED flood light
"Well said Dennis, try a lighting calculation for the space you need."
12 hours ago
Chris Laumer-Giddens's blog post was featured

Rock Wool Insulation for Floor of High Performance Tiny House

ROCK WOOL INSULATION FOR FLOOR OF HIGH PERFORMANCE TINY HOUSEIn August of 2016, we posted a video…See More
15 hours ago
Horace Douglas Hunt, Jr. joined Tom White's group
Thumbnail

Weatherization

Share your concerns and successes as a weatherization professional, or information for this…See More
17 hours ago
Horace Douglas Hunt, Jr. joined Sean Lintow Sr's group
Thumbnail

Best Practices (Residential)

Best Building, Retrofitting, or even Auditing Practices - what are they, what should change, what…See More
17 hours ago

Home Energy Pros

Welcome to Home Energy Pros – the unique digital community by and for those who work in the home energy performance arena.

Home Energy Pros was founded by the developers of Home Energy Saver Pro (supported by the U.S. Department of Energy) and brought to you in partnership with Home Energy magazine.  Home Energy Pros is sponsored by the Better Buildings Residential Network. Please honor our Guidelines

© 2017   Created by Lawrence Berkeley National Laboratory.   Powered by

Badges  |  Report an Issue  |  Terms of Service