I've encountered an install of 6" duct directly connected to the outside through the rim joist and covered by a simple mess screen on the end.  The other end has been placed next to the gas furnace as make-up air.  The cold air just pours in whether the furnace is active or not.  There is a clear need for make-up air as the CAZ is very small and the DHW and furnace are next within a couple of feet of each other.  Any advice on a simple mechanical option to better regulate this situation.  (The DHW is natural draft and the furnace is power-assist.  They are commonly vented.)   

Views: 212

Reply to This

Replies to This Discussion

Let it be known common venting of power draft and natural draft appliances is against code in many jurisdictions. Are the DWH and Furnace in conditioned or unconditioned space?

The units are in a conditioned laundry area, 16'X11'X7.5'  The DHW is 36K btu & furnace 45K btu. (Dryer is electric.)

Hi Jerry, your classic can of worms.

Each of us must decide where we will draw the line, that line where we can be blamed for making conditions worse and this is one.  Any improvements on air sealing could affect that CAZ, therefore, IMO, I advise the problems need to be fixed FIRST, before I will continue with an audit.  I usually catch these with a pre-audit visit, but that's my routine.

Here is some of what you face and I'm not a pro on HVAC as Maine prohibits auditors from doing anything beyond the specified CAZ test. 

1.  Venting as Bob mentioned needs to meet code.

2.  Replacement air also needs to meet code, such as vent area, high and low vents, and outside clearance.  A 6" duct is way too small.

3.  Any mechanical solutions need to be approved for that use, no shoe strings and cloths pins.

A common recommendation is a cold air trap with a bucket or a 180° turn in the incoming duct.  The short explanation is, they don't do as advertised and neither would bring the venting up to code.

Most burner units, and you have two, have combustion air kits that can draw air directly from the outside.  There are also powered dampers which open and close as needed and prevent the burner from coming on if they fail.  Whether either of these could be used to solve the problem and meet the codes would need to be determined.

Again, this is my opinion and perhaps others will chime in with some code requirements, beyond my scope.

Bud

Picture of uncontrolled make-up air duct next to furnace.

 

Attachments:

Glad they used insulated duct for the fresh air intake ;)

Have you considered sectioning off the water heater and furnace from the rest of the laundry area? Make the that unconditioned space. How about a vent between the laundry area and the rest of the house effectively increasing the size of the laundry room and eliminating the need for make up air?

Be sure to check local codes before making a final choice. As Bud said this may be a HVAC contractors issue, although I probably wouldn't call the one that stuck in the 6" flex for fresh air...

RSS

Home Energy Pros

Home Energy Pros was founded by the developers of Home Energy Saver Pro (sponsored by the U.S. Department of Energy,) and brought to you in partnership with Home Energy magazine.

Latest Activity

Hal Skinner replied to Richard Beyer's discussion Spontaneous Combustion and Flash Fire regarding Spray Foam Insulation
"Richard, here is something else that might be pertinent. In my hundreds of conversations with our…"
14 minutes ago
Trip posted a discussion

Starting a Home Weatherization Business. Considering it...

I am considering starting a home weatherization business. (I live in Southeast Alabama)  Currently…See More
52 minutes ago
Jim Gunshinan commented on Jim Gunshinan's blog post My Energy Upgrade California—The Numbers Are In
"To all, one thing I don't lack is advice from the experts! Thanks for the input, challenges,…"
1 hour ago
tedkidd commented on Jim Gunshinan's blog post My Energy Upgrade California—The Numbers Are In
"Jim, I'm glad you are open, that's great!  We all learn best when we are open! The…"
2 hours ago
David Eakin commented on Jim Gunshinan's blog post My Energy Upgrade California—The Numbers Are In
"Jim, Well, as the editor of Home Energy you should already know that the order of remediation is…"
2 hours ago
Greg Labbe posted a blog post

Technical Tape Desecration

Lets face it – building science is pushing the performance of adhesive tapes to a new levels and…See More
4 hours ago
Stacy Hunt posted an event

High Performance Enclosure Strategies: Part II, New Construction at Online

August 13, 2014 from 1pm to 2:30pm
Please join the Building America Program for our free webinar: High Performance Enclosure…See More
5 hours ago
Richard Beyer replied to Howard Katzman's discussion UV lights on filters
"Howard, There are numerous manufacturer's who swear these systems work and then you have the…"
14 hours ago
Christopher Morin posted a blog post

How do You Test a TXV?

  Thermostatic Expansion Valves (TEV or TXV), one of the most popular metering devices for…See More
17 hours ago
Howard Katzman posted a discussion

UV lights on filters

I recently saw UV bulb installations in 2 HVAC systems in a home. Each system had the Lennox…See More
20 hours ago
Don Fitchett joined Michael Stuart's group
Thumbnail

INFRARED THERMOGRAPHY USERS

This group is dedicated to knowledge sharing and discussion of infrared thermography for building…See More
20 hours ago
Don Fitchett commented on Diane Chojnowski's group Pinterest
"While most of our (BIN95.com) energy post and boards are industrial related, there are crossovers…"
20 hours ago

© 2014   Created by Lawrence Berkeley National Laboratory.

Badges  |  Report an Issue  |  Terms of Service