I've encountered an install of 6" duct directly connected to the outside through the rim joist and covered by a simple mess screen on the end.  The other end has been placed next to the gas furnace as make-up air.  The cold air just pours in whether the furnace is active or not.  There is a clear need for make-up air as the CAZ is very small and the DHW and furnace are next within a couple of feet of each other.  Any advice on a simple mechanical option to better regulate this situation.  (The DHW is natural draft and the furnace is power-assist.  They are commonly vented.)   

Views: 332

Reply to This

Replies to This Discussion

Let it be known common venting of power draft and natural draft appliances is against code in many jurisdictions. Are the DWH and Furnace in conditioned or unconditioned space?

The units are in a conditioned laundry area, 16'X11'X7.5'  The DHW is 36K btu & furnace 45K btu. (Dryer is electric.)

Hi Jerry, your classic can of worms.

Each of us must decide where we will draw the line, that line where we can be blamed for making conditions worse and this is one.  Any improvements on air sealing could affect that CAZ, therefore, IMO, I advise the problems need to be fixed FIRST, before I will continue with an audit.  I usually catch these with a pre-audit visit, but that's my routine.

Here is some of what you face and I'm not a pro on HVAC as Maine prohibits auditors from doing anything beyond the specified CAZ test. 

1.  Venting as Bob mentioned needs to meet code.

2.  Replacement air also needs to meet code, such as vent area, high and low vents, and outside clearance.  A 6" duct is way too small.

3.  Any mechanical solutions need to be approved for that use, no shoe strings and cloths pins.

A common recommendation is a cold air trap with a bucket or a 180° turn in the incoming duct.  The short explanation is, they don't do as advertised and neither would bring the venting up to code.

Most burner units, and you have two, have combustion air kits that can draw air directly from the outside.  There are also powered dampers which open and close as needed and prevent the burner from coming on if they fail.  Whether either of these could be used to solve the problem and meet the codes would need to be determined.

Again, this is my opinion and perhaps others will chime in with some code requirements, beyond my scope.

Bud

Picture of uncontrolled make-up air duct next to furnace.

 

Attachments:

Glad they used insulated duct for the fresh air intake ;)

Have you considered sectioning off the water heater and furnace from the rest of the laundry area? Make the that unconditioned space. How about a vent between the laundry area and the rest of the house effectively increasing the size of the laundry room and eliminating the need for make up air?

Be sure to check local codes before making a final choice. As Bud said this may be a HVAC contractors issue, although I probably wouldn't call the one that stuck in the 6" flex for fresh air...

RSS

Videos

  • Add Videos
  • View All

Twitter

Latest Activity

Nate Adams replied to Rob Madden, Solar Home Broker's discussion Indoor Air Quality Monitors and Meters
"Rob, I've bought, borrowed, or been given a number of different monitors. I had an Air Advice…"
1 hour ago
tedkidd replied to Rob Madden, Solar Home Broker's discussion Indoor Air Quality Monitors and Meters
"Yep, steep price but you will learn a lot. We are hoping these new devices that homeowners can own…"
1 hour ago
tedkidd replied to Luis Hernandez's discussion ERV Configuration
"We don't recommend ERV's anymore. If you are in a green grass climate ventilating…"
2 hours ago
Home Energy Magazine's blog post was featured

Is the Perfect Wall Realistic?

Wrong question. The right…See More
2 hours ago
Chris Laumer-Giddens's blog post was featured

Building with Rocks, Rocks. Check out the Drying Potential

Building with Rocks, Rocks! Check out the Drying Potential.Check this out! This 24" x 48" x 2"…See More
2 hours ago
Dan McKee posted a blog post

Innovations for Heating and Cooling

Heating and cooling of indoor spaces is one of the major operations of modern households and…See More
7 hours ago
Amber Vignieri posted a status
"In the market for a #solar home? We're bringing you improved solar #MLS listings. http://bit.ly/2auldQ8"
yesterday
Tom White's video was featured

CalCERTS Plenum Pressure Matching

This video describes how to perform plenum pressure matching to measure system airflow.
yesterday

© 2016   Created by Lawrence Berkeley National Laboratory.   Powered by

Badges  |  Report an Issue  |  Terms of Service