I've encountered an install of 6" duct directly connected to the outside through the rim joist and covered by a simple mess screen on the end.  The other end has been placed next to the gas furnace as make-up air.  The cold air just pours in whether the furnace is active or not.  There is a clear need for make-up air as the CAZ is very small and the DHW and furnace are next within a couple of feet of each other.  Any advice on a simple mechanical option to better regulate this situation.  (The DHW is natural draft and the furnace is power-assist.  They are commonly vented.)   

Views: 357

Reply to This

Replies to This Discussion

Let it be known common venting of power draft and natural draft appliances is against code in many jurisdictions. Are the DWH and Furnace in conditioned or unconditioned space?

The units are in a conditioned laundry area, 16'X11'X7.5'  The DHW is 36K btu & furnace 45K btu. (Dryer is electric.)

Hi Jerry, your classic can of worms.

Each of us must decide where we will draw the line, that line where we can be blamed for making conditions worse and this is one.  Any improvements on air sealing could affect that CAZ, therefore, IMO, I advise the problems need to be fixed FIRST, before I will continue with an audit.  I usually catch these with a pre-audit visit, but that's my routine.

Here is some of what you face and I'm not a pro on HVAC as Maine prohibits auditors from doing anything beyond the specified CAZ test. 

1.  Venting as Bob mentioned needs to meet code.

2.  Replacement air also needs to meet code, such as vent area, high and low vents, and outside clearance.  A 6" duct is way too small.

3.  Any mechanical solutions need to be approved for that use, no shoe strings and cloths pins.

A common recommendation is a cold air trap with a bucket or a 180° turn in the incoming duct.  The short explanation is, they don't do as advertised and neither would bring the venting up to code.

Most burner units, and you have two, have combustion air kits that can draw air directly from the outside.  There are also powered dampers which open and close as needed and prevent the burner from coming on if they fail.  Whether either of these could be used to solve the problem and meet the codes would need to be determined.

Again, this is my opinion and perhaps others will chime in with some code requirements, beyond my scope.

Bud

Picture of uncontrolled make-up air duct next to furnace.

 

Attachments:

Glad they used insulated duct for the fresh air intake ;)

Have you considered sectioning off the water heater and furnace from the rest of the laundry area? Make the that unconditioned space. How about a vent between the laundry area and the rest of the house effectively increasing the size of the laundry room and eliminating the need for make up air?

Be sure to check local codes before making a final choice. As Bud said this may be a HVAC contractors issue, although I probably wouldn't call the one that stuck in the 6" flex for fresh air...

RSS

Videos

  • Add Videos
  • View All

Latest Activity

Kim added a discussion to the group Job Board
Thumbnail

QA Weatherization Field Inspector Philadelphia or Northern New Jersey

QA Weatherization Field Inspector (Phila. Or Northern New Jersey)Are you looking for a…See More
1 hour ago
Barbara Smith's video was featured

Advanced framing techniques

In some ways building a new house hasn't changed much over the last 100 years. Some builders are changing the way a home is constructed to make sure the hous... From Alliant Energy PowerHouse TV Channel on YouTube
1 hour ago
Kim joined Diane Chojnowski's group
Thumbnail

Job Board

This group is for posting jobs related to all aspects of the home performance industry including…See More
1 hour ago
Profile IconKim, Brandon Robidoux, Damon Morales and 3 more joined Home Energy Pros
3 hours ago
Michael Woodham posted a photo

Shelves & Cabinets Maker - Spaceworks Design

Renovate your Home & Office by installing Shelves and Custom Cabinets!Stunning Home &…
12 hours ago
Thermodyne Boilers posted a discussion

Major problems which can cause troubles in Boilers

Most boilers come with a manufacturer’s warranty.…See More
12 hours ago
Kevin Daly added a discussion to the group Energy Auditing Equipment for Sale, Trade or to Purchase
Thumbnail

Minneapolis Blower Door Model 3 for sale

Selling minimally used Minneapolis Blower Door DG-700 model 3. Includes model 3 fan, DG-700…See More
18 hours ago
marius gherman posted a video

Winter conditions, perfect operation - ROTEX / DAIKIN heat pump

FIAMMA company, ROTEX partner in Romania, offering turnkey packages to improve energy efficiency, from supply to installation. With an experience of over 25 ...
yesterday

Home Energy Pros

Welcome to Home Energy Pros – the unique digital community by and for those who work in the home energy performance arena.

Home Energy Pros was founded by the developers of Home Energy Saver Pro (supported by the U.S. Department of Energy) and brought to you in partnership with Home Energy magazine.  Home Energy Pros is sponsored by the Better Buildings Residential Network. Please honor our Guidelines

© 2017   Created by Lawrence Berkeley National Laboratory.   Powered by

Badges  |  Report an Issue  |  Terms of Service