I've encountered an install of 6" duct directly connected to the outside through the rim joist and covered by a simple mess screen on the end.  The other end has been placed next to the gas furnace as make-up air.  The cold air just pours in whether the furnace is active or not.  There is a clear need for make-up air as the CAZ is very small and the DHW and furnace are next within a couple of feet of each other.  Any advice on a simple mechanical option to better regulate this situation.  (The DHW is natural draft and the furnace is power-assist.  They are commonly vented.)   

Views: 200

Reply to This

Replies to This Discussion

Let it be known common venting of power draft and natural draft appliances is against code in many jurisdictions. Are the DWH and Furnace in conditioned or unconditioned space?

The units are in a conditioned laundry area, 16'X11'X7.5'  The DHW is 36K btu & furnace 45K btu. (Dryer is electric.)

Hi Jerry, your classic can of worms.

Each of us must decide where we will draw the line, that line where we can be blamed for making conditions worse and this is one.  Any improvements on air sealing could affect that CAZ, therefore, IMO, I advise the problems need to be fixed FIRST, before I will continue with an audit.  I usually catch these with a pre-audit visit, but that's my routine.

Here is some of what you face and I'm not a pro on HVAC as Maine prohibits auditors from doing anything beyond the specified CAZ test. 

1.  Venting as Bob mentioned needs to meet code.

2.  Replacement air also needs to meet code, such as vent area, high and low vents, and outside clearance.  A 6" duct is way too small.

3.  Any mechanical solutions need to be approved for that use, no shoe strings and cloths pins.

A common recommendation is a cold air trap with a bucket or a 180° turn in the incoming duct.  The short explanation is, they don't do as advertised and neither would bring the venting up to code.

Most burner units, and you have two, have combustion air kits that can draw air directly from the outside.  There are also powered dampers which open and close as needed and prevent the burner from coming on if they fail.  Whether either of these could be used to solve the problem and meet the codes would need to be determined.

Again, this is my opinion and perhaps others will chime in with some code requirements, beyond my scope.

Bud

Picture of uncontrolled make-up air duct next to furnace.

 

Attachments:

Glad they used insulated duct for the fresh air intake ;)

Have you considered sectioning off the water heater and furnace from the rest of the laundry area? Make the that unconditioned space. How about a vent between the laundry area and the rest of the house effectively increasing the size of the laundry room and eliminating the need for make up air?

Be sure to check local codes before making a final choice. As Bud said this may be a HVAC contractors issue, although I probably wouldn't call the one that stuck in the 6" flex for fresh air...

RSS

Home Energy Pros

Home Energy Pros was founded by the developers of Home Energy Saver Pro (sponsored by the U.S. Department of Energy,) and brought to you in partnership with Home Energy magazine.

Latest Activity

Mst. Fatema Aktar is now a member of Home Energy Pros
3 hours ago
Robert Leone added a discussion to the group Energy Auditing Equipment for Sale, Trade or to Purchase
Thumbnail

Blower Door Package for Sale

Hi,I am selling my blower door with extras as a package or individually. These items are used but…See More
10 hours ago
Profile IconRobert Leone and Richard Vito joined allen p tanner's group
Thumbnail

Energy Auditing Equipment for Sale, Trade or to Purchase

Discuss the pros and cons of the equipment you are interested in prior to purchase. Post equipment…See More
10 hours ago
Richard Vito joined Sean Lintow Sr's group
Thumbnail

Best Practices (Residential)

Best Building, Retrofitting, or even Auditing Practices - what are they, what should change, what…See More
18 hours ago
Richard Vito joined James Sayers's group
Thumbnail

Marketing Energy Efficiency

Sharing ideas, tools and examples of promoting energy efficiency to consumersSee More
18 hours ago
Richard Vito joined Allison A. Bailes III's group
Thumbnail

HVAC

HVAC design, Manuals J, S, T, & D, Duct leakage, Air flow, ENERGY STAR new home requirements,…See More
18 hours ago
Richard Vito joined Kyle Brown's group
Thumbnail

Wrightsoft - Manual J / Manual D

If you use Wrightsoft to calculate loads or design ducts, you likely have questions.  Get answers…See More
18 hours ago
Jim Gunshinan commented on Jim Gunshinan's blog post Energy Upgrade California—Up Close and Personal
"I had a revelation while attending Bruce Manclark's session of duct leak testing at the Energy…"
yesterday
George J. Nesbitt commented on Jim Gunshinan's blog post Energy Upgrade California—Up Close and Personal
"Blower Door; the 2007 test was a depressurization test, and the 2014 a pressurization test, which…"
yesterday
George J. Nesbitt replied to Kaushal Bharath Raju's discussion Affordability & Deep Energy Upgrade/Passive House Retrofit in Berkeley, California.
"Plan, plan, plan, plan. The 1st step to is to understand the house, how it's built, the…"
yesterday
George J. Nesbitt posted an event

High Performance Windows - A Panel of Experts at Pyramid Alehouse`

April 26, 2014 from 3pm to 5pm
Join a lively panel discussion on high performance windows. We'll cover some basics, as well as…See More
yesterday
Kaushal Bharath Raju replied to Kaushal Bharath Raju's discussion Affordability & Deep Energy Upgrade/Passive House Retrofit in Berkeley, California.
"Hi David, Thanks for pointing out Martin Holiday's article. I do not wish to engage in the…"
yesterday

© 2014   Created by Lawrence Berkeley National Laboratory.

Badges  |  Report an Issue  |  Terms of Service