I've encountered an install of 6" duct directly connected to the outside through the rim joist and covered by a simple mess screen on the end.  The other end has been placed next to the gas furnace as make-up air.  The cold air just pours in whether the furnace is active or not.  There is a clear need for make-up air as the CAZ is very small and the DHW and furnace are next within a couple of feet of each other.  Any advice on a simple mechanical option to better regulate this situation.  (The DHW is natural draft and the furnace is power-assist.  They are commonly vented.)   

Views: 217

Reply to This

Replies to This Discussion

Let it be known common venting of power draft and natural draft appliances is against code in many jurisdictions. Are the DWH and Furnace in conditioned or unconditioned space?

The units are in a conditioned laundry area, 16'X11'X7.5'  The DHW is 36K btu & furnace 45K btu. (Dryer is electric.)

Hi Jerry, your classic can of worms.

Each of us must decide where we will draw the line, that line where we can be blamed for making conditions worse and this is one.  Any improvements on air sealing could affect that CAZ, therefore, IMO, I advise the problems need to be fixed FIRST, before I will continue with an audit.  I usually catch these with a pre-audit visit, but that's my routine.

Here is some of what you face and I'm not a pro on HVAC as Maine prohibits auditors from doing anything beyond the specified CAZ test. 

1.  Venting as Bob mentioned needs to meet code.

2.  Replacement air also needs to meet code, such as vent area, high and low vents, and outside clearance.  A 6" duct is way too small.

3.  Any mechanical solutions need to be approved for that use, no shoe strings and cloths pins.

A common recommendation is a cold air trap with a bucket or a 180° turn in the incoming duct.  The short explanation is, they don't do as advertised and neither would bring the venting up to code.

Most burner units, and you have two, have combustion air kits that can draw air directly from the outside.  There are also powered dampers which open and close as needed and prevent the burner from coming on if they fail.  Whether either of these could be used to solve the problem and meet the codes would need to be determined.

Again, this is my opinion and perhaps others will chime in with some code requirements, beyond my scope.

Bud

Picture of uncontrolled make-up air duct next to furnace.

 

Attachments:

Glad they used insulated duct for the fresh air intake ;)

Have you considered sectioning off the water heater and furnace from the rest of the laundry area? Make the that unconditioned space. How about a vent between the laundry area and the rest of the house effectively increasing the size of the laundry room and eliminating the need for make up air?

Be sure to check local codes before making a final choice. As Bud said this may be a HVAC contractors issue, although I probably wouldn't call the one that stuck in the 6" flex for fresh air...

RSS

Home Energy Pros

Home Energy Pros was founded by the developers of Home Energy Saver Pro (sponsored by the U.S. Department of Energy,) and brought to you in partnership with Home Energy magazine.

Latest Activity

Susan E. Buchan's event was featured

EEBA Excellence in Building Conference at Doubletree Union Station Hotel

September 23, 2014 at 8am to September 25, 2014 at 2pm
13 hours ago
Susan E. Buchan posted an event

EEBA Excellence in Building Conference at Doubletree Union Station Hotel

September 23, 2014 at 8am to September 25, 2014 at 2pm
14 hours ago
Rem Husted replied to Andy Gostisha's discussion Disguising Ductless Heat Pump Units
"I think most consumers wouldn't want a big box called a refrigerator or a stove or…"
14 hours ago
Scott Katznelson replied to Scott Katznelson's discussion Database of zip code or county by climate zone
"You know those maps you can find for energy code climate zone specific reference.  That's…"
15 hours ago
JEFFREY M HUGO, CBO replied to Richard Beyer's discussion Sprinkler Mandate Debated.. What do you think should be done?
"Fire sprinklers operate when the fires are small. Typically it only takes approx 20 gallons per…"
15 hours ago
Scott Katznelson replied to Scott Katznelson's discussion Database of zip code or county by climate zone
"Thanks.  That's the best source I've yet found, and maybe the best that's out…"
15 hours ago
Diane Chojnowski replied to Scott Katznelson's discussion Database of zip code or county by climate zone
"I posted the question on HEP's facebook page and Bill Spohn commented: Try…"
17 hours ago
Profile IconKevin Jordan, Hannah Strong, Rich Snyder and 1 more joined Home Energy Pros
yesterday

© 2014   Created by Lawrence Berkeley National Laboratory.

Badges  |  Report an Issue  |  Terms of Service