I've encountered an install of 6" duct directly connected to the outside through the rim joist and covered by a simple mess screen on the end.  The other end has been placed next to the gas furnace as make-up air.  The cold air just pours in whether the furnace is active or not.  There is a clear need for make-up air as the CAZ is very small and the DHW and furnace are next within a couple of feet of each other.  Any advice on a simple mechanical option to better regulate this situation.  (The DHW is natural draft and the furnace is power-assist.  They are commonly vented.)   

Views: 323

Reply to This

Replies to This Discussion

Let it be known common venting of power draft and natural draft appliances is against code in many jurisdictions. Are the DWH and Furnace in conditioned or unconditioned space?

The units are in a conditioned laundry area, 16'X11'X7.5'  The DHW is 36K btu & furnace 45K btu. (Dryer is electric.)

Hi Jerry, your classic can of worms.

Each of us must decide where we will draw the line, that line where we can be blamed for making conditions worse and this is one.  Any improvements on air sealing could affect that CAZ, therefore, IMO, I advise the problems need to be fixed FIRST, before I will continue with an audit.  I usually catch these with a pre-audit visit, but that's my routine.

Here is some of what you face and I'm not a pro on HVAC as Maine prohibits auditors from doing anything beyond the specified CAZ test. 

1.  Venting as Bob mentioned needs to meet code.

2.  Replacement air also needs to meet code, such as vent area, high and low vents, and outside clearance.  A 6" duct is way too small.

3.  Any mechanical solutions need to be approved for that use, no shoe strings and cloths pins.

A common recommendation is a cold air trap with a bucket or a 180° turn in the incoming duct.  The short explanation is, they don't do as advertised and neither would bring the venting up to code.

Most burner units, and you have two, have combustion air kits that can draw air directly from the outside.  There are also powered dampers which open and close as needed and prevent the burner from coming on if they fail.  Whether either of these could be used to solve the problem and meet the codes would need to be determined.

Again, this is my opinion and perhaps others will chime in with some code requirements, beyond my scope.

Bud

Picture of uncontrolled make-up air duct next to furnace.

 

Attachments:

Glad they used insulated duct for the fresh air intake ;)

Have you considered sectioning off the water heater and furnace from the rest of the laundry area? Make the that unconditioned space. How about a vent between the laundry area and the rest of the house effectively increasing the size of the laundry room and eliminating the need for make up air?

Be sure to check local codes before making a final choice. As Bud said this may be a HVAC contractors issue, although I probably wouldn't call the one that stuck in the 6" flex for fresh air...

RSS

Videos

  • Add Videos
  • View All

Twitter

Latest Activity

Tom White's video was featured

Robby Schwarz on Builder Collaboration

Hear Robby Schwarz, of EnergyLogic discuss the value Owens Corning brings to Thrive Home Builders.
38 minutes ago
Profile IconLights N More, John Kamas and Chuck Santeler joined Home Energy Pros
2 hours ago
Crosbey Archery liked Don Hynek's discussion Testing "Magic Pak" units??
2 hours ago
Crosbey Archery joined Norm Bourassa's group
Thumbnail

Multifamily Buildings

For too long there has been relatively little EE focus on multifamily, but some new programs have…See More
2 hours ago
Crosbey Archery liked Crosbey Archery's blog post Energy Tips - Fresh Look at Heating and Cooling the Home
3 hours ago
tedkidd liked Luis Hernandez's discussion Airsealing an old basement ceiling
9 hours ago
Ryan T De La Rosa posted a blog post

The Clean Power Plan and What You Can Do

Last month, Jessica Hardcastle at Environment Leader described an especially non-polarizing…See More
11 hours ago
Ed Minch replied to Luis Hernandez's discussion Airsealing an old basement ceiling
"Luis Think of it as a part of the house that is not being used, but part of the house none the…"
15 hours ago

© 2016   Created by Lawrence Berkeley National Laboratory.   Powered by

Badges  |  Report an Issue  |  Terms of Service