I've encountered an install of 6" duct directly connected to the outside through the rim joist and covered by a simple mess screen on the end.  The other end has been placed next to the gas furnace as make-up air.  The cold air just pours in whether the furnace is active or not.  There is a clear need for make-up air as the CAZ is very small and the DHW and furnace are next within a couple of feet of each other.  Any advice on a simple mechanical option to better regulate this situation.  (The DHW is natural draft and the furnace is power-assist.  They are commonly vented.)   

Views: 262

Reply to This

Replies to This Discussion

Let it be known common venting of power draft and natural draft appliances is against code in many jurisdictions. Are the DWH and Furnace in conditioned or unconditioned space?

The units are in a conditioned laundry area, 16'X11'X7.5'  The DHW is 36K btu & furnace 45K btu. (Dryer is electric.)

Hi Jerry, your classic can of worms.

Each of us must decide where we will draw the line, that line where we can be blamed for making conditions worse and this is one.  Any improvements on air sealing could affect that CAZ, therefore, IMO, I advise the problems need to be fixed FIRST, before I will continue with an audit.  I usually catch these with a pre-audit visit, but that's my routine.

Here is some of what you face and I'm not a pro on HVAC as Maine prohibits auditors from doing anything beyond the specified CAZ test. 

1.  Venting as Bob mentioned needs to meet code.

2.  Replacement air also needs to meet code, such as vent area, high and low vents, and outside clearance.  A 6" duct is way too small.

3.  Any mechanical solutions need to be approved for that use, no shoe strings and cloths pins.

A common recommendation is a cold air trap with a bucket or a 180° turn in the incoming duct.  The short explanation is, they don't do as advertised and neither would bring the venting up to code.

Most burner units, and you have two, have combustion air kits that can draw air directly from the outside.  There are also powered dampers which open and close as needed and prevent the burner from coming on if they fail.  Whether either of these could be used to solve the problem and meet the codes would need to be determined.

Again, this is my opinion and perhaps others will chime in with some code requirements, beyond my scope.

Bud

Picture of uncontrolled make-up air duct next to furnace.

 

Attachments:

Glad they used insulated duct for the fresh air intake ;)

Have you considered sectioning off the water heater and furnace from the rest of the laundry area? Make the that unconditioned space. How about a vent between the laundry area and the rest of the house effectively increasing the size of the laundry room and eliminating the need for make up air?

Be sure to check local codes before making a final choice. As Bud said this may be a HVAC contractors issue, although I probably wouldn't call the one that stuck in the 6" flex for fresh air...

RSS

Home Energy Pros

Home Energy Pros was founded by the developers of Home Energy Saver Pro (sponsored by the U.S. Department of Energy,) and brought to you in partnership with Home Energy magazine.  Home Energy Pros is sponsored by the Better Buildings Residential Network.

Latest Activity

William H Nickerson replied to Kim Tanner's discussion Fantastic innovation
"So that's where you use those True Flow plates....."
1 hour ago
Colin Genge updated an event
Thumbnail

Passive House Testing Webinar with Kevin Brennan of the Passive House Academy at Online

September 29, 2015 from 1pm to 2pm
Tests needed to qualify as a passive houseWhy we’re seeing an increase in PH buildingsBest…See More
8 hours ago
Colin Genge updated an event
Thumbnail

DM32 Smart Gauge 101 Webinar at Online

September 22, 2015 from 1pm to 2pm
Webinar Learning Objectives:Gauge settings and operationCalculate results in the gaugeUpdate the…See More
8 hours ago
Colin Genge updated an event
Thumbnail

Blower Door 101 Webinar at Online

September 15, 2015 from 1pm to 2pm
See how easy it is to do your first test. Learn tips to perform your first duct test in only twenty…See More
8 hours ago
Colin Genge updated an event
Thumbnail

Zone Pressure Diagnostics (ZPD) with Bill Eckman of NME$A Webinar at Online

September 10, 2015 from 1pm to 2pm
Benefits and limitations of Zonal Pressure Diagnostics (ZPD).Best practices for accurate…See More
8 hours ago
Colin Genge updated an event
Thumbnail

Problem Solving- Air Tightness Tests of Large Buildings Webinar at Online

September 1, 2015 from 1pm to 2pm
Effect of Stack Pressure during airtightness tests in tall buildings-caluculating the effectsHow…See More
8 hours ago
Kim Tanner posted a discussion

Fantastic innovation

What an awesome example of fantastic innovation!Check out the TrueFlow Capture Box CEE made!…See More
9 hours ago
Amina Lang posted events
10 hours ago

© 2015   Created by Lawrence Berkeley National Laboratory.

Badges  |  Report an Issue  |  Terms of Service