I've encountered an install of 6" duct directly connected to the outside through the rim joist and covered by a simple mess screen on the end.  The other end has been placed next to the gas furnace as make-up air.  The cold air just pours in whether the furnace is active or not.  There is a clear need for make-up air as the CAZ is very small and the DHW and furnace are next within a couple of feet of each other.  Any advice on a simple mechanical option to better regulate this situation.  (The DHW is natural draft and the furnace is power-assist.  They are commonly vented.)   

Views: 213

Reply to This

Replies to This Discussion

Let it be known common venting of power draft and natural draft appliances is against code in many jurisdictions. Are the DWH and Furnace in conditioned or unconditioned space?

The units are in a conditioned laundry area, 16'X11'X7.5'  The DHW is 36K btu & furnace 45K btu. (Dryer is electric.)

Hi Jerry, your classic can of worms.

Each of us must decide where we will draw the line, that line where we can be blamed for making conditions worse and this is one.  Any improvements on air sealing could affect that CAZ, therefore, IMO, I advise the problems need to be fixed FIRST, before I will continue with an audit.  I usually catch these with a pre-audit visit, but that's my routine.

Here is some of what you face and I'm not a pro on HVAC as Maine prohibits auditors from doing anything beyond the specified CAZ test. 

1.  Venting as Bob mentioned needs to meet code.

2.  Replacement air also needs to meet code, such as vent area, high and low vents, and outside clearance.  A 6" duct is way too small.

3.  Any mechanical solutions need to be approved for that use, no shoe strings and cloths pins.

A common recommendation is a cold air trap with a bucket or a 180° turn in the incoming duct.  The short explanation is, they don't do as advertised and neither would bring the venting up to code.

Most burner units, and you have two, have combustion air kits that can draw air directly from the outside.  There are also powered dampers which open and close as needed and prevent the burner from coming on if they fail.  Whether either of these could be used to solve the problem and meet the codes would need to be determined.

Again, this is my opinion and perhaps others will chime in with some code requirements, beyond my scope.

Bud

Picture of uncontrolled make-up air duct next to furnace.

 

Attachments:

Glad they used insulated duct for the fresh air intake ;)

Have you considered sectioning off the water heater and furnace from the rest of the laundry area? Make the that unconditioned space. How about a vent between the laundry area and the rest of the house effectively increasing the size of the laundry room and eliminating the need for make up air?

Be sure to check local codes before making a final choice. As Bud said this may be a HVAC contractors issue, although I probably wouldn't call the one that stuck in the 6" flex for fresh air...

RSS

Home Energy Pros

Home Energy Pros was founded by the developers of Home Energy Saver Pro (sponsored by the U.S. Department of Energy,) and brought to you in partnership with Home Energy magazine.

Latest Activity

Tom Conlon's discussion was featured

Whole House Fans - Love 'Em or Not?

I just searched this forum for "Whole House Fan", but I didn't find much about them (except …See More
40 minutes ago
Tom White shared Brandon Walton's blog post on Twitter
44 minutes ago
Brandon Walton's blog post was featured

12 Things Every Home Performance Contractor Should Have on Their Work Truck

Every home is unique and differs from the last. It would be a perfect world (from a project…See More
44 minutes ago
Griffin Hagle replied to Tom Conlon's discussion Whole House Fans - Love 'Em or Not?
2 hours ago
Griffin Hagle replied to Tom Conlon's discussion Whole House Fans - Love 'Em or Not?
"Kurt, Whoops, looks like I got my links mixed up. Thanks for pointing that out. Here's the…"
2 hours ago
Kurt Shafer replied to Tom Conlon's discussion Whole House Fans - Love 'Em or Not?
"Glen,  I went to Homepower.com and did a search for whole house fan. Could not find that…"
2 hours ago
Glen Gallo replied to Tom Conlon's discussion Whole House Fans - Love 'Em or Not?
"I no longer have my subscription to the Home Power Magazine but these figures were pulled from the…"
2 hours ago
Kurt Shafer replied to Tom Conlon's discussion Whole House Fans - Love 'Em or Not?
"Glen,  I read your blog with some interest.  You say  " Per the Home…"
3 hours ago
tedkidd commented on Scott Mellberg's blog post Lessons from Energy Efficiency Advisors: Getting Homeowners Onboard with Home Performance
"OMG, you are one of those myopic thinkers are you? Others do it better therefore drastic action is…"
3 hours ago
Glen Gallo replied to Tom Conlon's discussion Whole House Fans - Love 'Em or Not?
"I do not like them and I am in Southern California. I think the whole house fan in prescriptive…"
3 hours ago
Kurt Shafer replied to Tom Conlon's discussion Whole House Fans - Love 'Em or Not?
"Griffin,  Is this really the link you…"
4 hours ago
Kurt Shafer replied to Tom Conlon's discussion Whole House Fans - Love 'Em or Not?
"Tom, great new post! Thank you for the focus. As you know, the term "whole house fan" is…"
4 hours ago

© 2014   Created by Lawrence Berkeley National Laboratory.

Badges  |  Report an Issue  |  Terms of Service