Unless I have this wrong, the BPI CAZ depressurization limits and draft calculations are for gas boilers and furnaces.  Up here in New England we have a lot of oil burners.  It would seem that it would take a lot more negative pressure in a CAZ to get an oil burner to spill.  I have flue pressures for oil of: <10 F at -15 Pa, 11 - 40F at -13 Pa, 41 - 60F at -11 Pa, 61 - 90F at -9 Pa, and >90F at -7Pa.

Tags: Oil, burner, limits, pressure

Views: 286

Reply to This

Replies to This Discussion

Paul,
We see lots of fuel oil in the NC mountains where we have been training BPI for over 2.5 years now. After many discussions with several trainers i have come to the conclusion that the fuel oil burner should be classified the same as an induced fan furnace receiving a CAZ Depressurization limit of -15. However, High Retention Head Burners may allow this limit to go even lower. I would love an official BPI interpretation on this issue.
I have recently received a reply from Tony Peters QA for Affiliates for BPI who states that, "CAZ depressurization limits shall be identical for gas or oil fueled combustion appliances. An oil fueled combustion appliance shall not be classified as a mechanically assisted draft appliance. Please classify oil fueled combustion appliances as natural draft boilers or furnaces." He also says, "Draft calculations shall also be identical for oil or gas fueled combustion appliances. Please follow the acceptable draft test results chart found on page 10 of BA for all natural draft appliances."
Seems a bit odd to me, but he explains that, "if the oil fueled combustion appliance has been installed with a barometric damper connected to the vent pipe, it cannot support a -15Pa CAZ depressurization limit."

RSS

Home Energy Pros

Home Energy Pros was founded by the developers of Home Energy Saver Pro (sponsored by the U.S. Department of Energy,) and brought to you in partnership with Home Energy magazine.  Home Energy Pros is sponsored by the Better Buildings Residential Network.

Latest Activity

Profile IconJerrad Pierce, tracylee, Nevada Heating and 4 more joined Home Energy Pros
8 hours ago
Shawn Weeks posted a blog post
8 hours ago
Kirsten Richnavsky's discussion was featured

New BPI Standard for Conducting Energy Audits Published as an ANSI Standard!

The Standard Practice for Basic Analysis of Buildings defines the minimum criteria and specific…See More
10 hours ago
Daniel Beauchemin's photo was featured

Residential installation of a ThermoDrain TD342B

DWHR HERS Index Score Credit Calculation ProcedureUntil such time that DWHR system calculations…
10 hours ago
Tom White's 2 videos were featured
10 hours ago
Corbett Lunsford's video was featured

New Home FAIL: Infrared Secrets Revealed

Building forensics guru Corbett Lunsford can show you what's behind the walls of any house- or are you afraid to find out? Don't be! It's all generally fixab...
10 hours ago
Jose Macho's blog post was featured

Why Don't Homeowners Spend Money on Energy Saving Upgrades??? Blame "Cognitive Biases"

A great transcript from a recent NPR "Morning Edition" broadcast about a recent California survey…See More
11 hours ago
Elizabeth Guinn's discussion was featured

ERV in need of backflow preventer.

I installed an ERV on my last job with the intake and exhaust utilizing 6" round hard duct.  I have…See More
11 hours ago

© 2015   Created by Lawrence Berkeley National Laboratory.

Badges  |  Report an Issue  |  Terms of Service