Unless I have this wrong, the BPI CAZ depressurization limits and draft calculations are for gas boilers and furnaces.  Up here in New England we have a lot of oil burners.  It would seem that it would take a lot more negative pressure in a CAZ to get an oil burner to spill.  I have flue pressures for oil of: <10 F at -15 Pa, 11 - 40F at -13 Pa, 41 - 60F at -11 Pa, 61 - 90F at -9 Pa, and >90F at -7Pa.

Tags: Oil, burner, limits, pressure

Views: 312

Reply to This

Replies to This Discussion

Paul,
We see lots of fuel oil in the NC mountains where we have been training BPI for over 2.5 years now. After many discussions with several trainers i have come to the conclusion that the fuel oil burner should be classified the same as an induced fan furnace receiving a CAZ Depressurization limit of -15. However, High Retention Head Burners may allow this limit to go even lower. I would love an official BPI interpretation on this issue.
I have recently received a reply from Tony Peters QA for Affiliates for BPI who states that, "CAZ depressurization limits shall be identical for gas or oil fueled combustion appliances. An oil fueled combustion appliance shall not be classified as a mechanically assisted draft appliance. Please classify oil fueled combustion appliances as natural draft boilers or furnaces." He also says, "Draft calculations shall also be identical for oil or gas fueled combustion appliances. Please follow the acceptable draft test results chart found on page 10 of BA for all natural draft appliances."
Seems a bit odd to me, but he explains that, "if the oil fueled combustion appliance has been installed with a barometric damper connected to the vent pipe, it cannot support a -15Pa CAZ depressurization limit."

RSS

Photos

Loading…
  • Add Photos
  • View All

Latest Activity

Sam Taylors replied to Quinn Korzeniecki's discussion 3 Energy Saving New Year’s Resolutions to Make in 2016
"Thanks for sharing Quinn, I enjoyed reading your 3 energy saving suggestions. How are you going…"
1 hour ago
Jonny Fisher joined allen p tanner's group
Thumbnail

Energy Auditing Equipment for Sale, Trade or to Purchase

Discuss the pros and cons of the equipment you are interested in prior to purchase. Post equipment…See More
5 hours ago
Profile IconJamie klema, James Weingardt and Anthony Adams joined Home Energy Pros
9 hours ago
Bob Blanchette liked Diane Chojnowski's discussion Now you can "LIKE" posts on Home Energy Pros!
11 hours ago
JC NATALE posted photos
yesterday
Joe Quiroz Jr. liked Don Hynek's discussion Superinsulation retrofit is Complete!
yesterday
Mick Lane replied to Rob Buchanan's discussion High-use headscratcher
"The geothermal heat pump is the most likely culprit.  The heat pump doesn't make heat it…"
Saturday
Mick Lane is now a member of Home Energy Pros
Friday

© 2016   Created by Lawrence Berkeley National Laboratory.   Powered by

Badges  |  Report an Issue  |  Terms of Service