Unless I have this wrong, the BPI CAZ depressurization limits and draft calculations are for gas boilers and furnaces.  Up here in New England we have a lot of oil burners.  It would seem that it would take a lot more negative pressure in a CAZ to get an oil burner to spill.  I have flue pressures for oil of: <10 F at -15 Pa, 11 - 40F at -13 Pa, 41 - 60F at -11 Pa, 61 - 90F at -9 Pa, and >90F at -7Pa.

Tags: Oil, burner, limits, pressure

Views: 299

Reply to This

Replies to This Discussion

Paul,
We see lots of fuel oil in the NC mountains where we have been training BPI for over 2.5 years now. After many discussions with several trainers i have come to the conclusion that the fuel oil burner should be classified the same as an induced fan furnace receiving a CAZ Depressurization limit of -15. However, High Retention Head Burners may allow this limit to go even lower. I would love an official BPI interpretation on this issue.
I have recently received a reply from Tony Peters QA for Affiliates for BPI who states that, "CAZ depressurization limits shall be identical for gas or oil fueled combustion appliances. An oil fueled combustion appliance shall not be classified as a mechanically assisted draft appliance. Please classify oil fueled combustion appliances as natural draft boilers or furnaces." He also says, "Draft calculations shall also be identical for oil or gas fueled combustion appliances. Please follow the acceptable draft test results chart found on page 10 of BA for all natural draft appliances."
Seems a bit odd to me, but he explains that, "if the oil fueled combustion appliance has been installed with a barometric damper connected to the vent pipe, it cannot support a -15Pa CAZ depressurization limit."

RSS

Home Energy Pros

Home Energy Pros was founded by the developers of Home Energy Saver Pro (sponsored by the U.S. Department of Energy,) and brought to you in partnership with Home Energy magazine.  Home Energy Pros is sponsored by the Better Buildings Residential Network.

Latest Activity

John Kaye posted a blog post

FREE Home Efficiency & Safety Assessments in the Los Angeles County area.

Since last June I have been qualifying homeowners in the Los Angeles County for the Home Upgrade…See More
3 hours ago
Eric Kjelshus replied to Rod Fox's discussion Does calcification affect electric water heater aquastat temperature sensor performance?
"Those 240 Volt aquastats shut off and then on kinda quick back on.  The older the tank the…"
8 hours ago
Profile IconMike Norvell Sr and Jen Loomis joined Home Energy Pros
13 hours ago
Rod Fox replied to Rod Fox's discussion Does calcification affect electric water heater aquastat temperature sensor performance?
"Well I'd love to tell you folks I found an answer, but I did not... I went to my…"
17 hours ago
Rod Fox replied to Kevin Eigel's discussion What is the best energy auditing software?
"I've been trying to answer this question for many years and have not yet found an answer.…"
17 hours ago
Jerry Lawrence posted events
17 hours ago
Jan Green commented on Theresa L Gilbride's blog post Find out who's building some of the best-performing homes in the country today with DOE’s Tour of Zero
"Thank you for sharing! "
19 hours ago
Jan Green commented on Theresa L Gilbride's blog post Find out who's building some of the best-performing homes in the country today with DOE’s Tour of Zero
"We have one builder in Arizona on the DOE list.  Good information for a blog!"
19 hours ago

© 2015   Created by Lawrence Berkeley National Laboratory.

Badges  |  Report an Issue  |  Terms of Service