Unless I have this wrong, the BPI CAZ depressurization limits and draft calculations are for gas boilers and furnaces.  Up here in New England we have a lot of oil burners.  It would seem that it would take a lot more negative pressure in a CAZ to get an oil burner to spill.  I have flue pressures for oil of: <10 F at -15 Pa, 11 - 40F at -13 Pa, 41 - 60F at -11 Pa, 61 - 90F at -9 Pa, and >90F at -7Pa.

Tags: Oil, burner, limits, pressure

Views: 280

Reply to This

Replies to This Discussion

Paul,
We see lots of fuel oil in the NC mountains where we have been training BPI for over 2.5 years now. After many discussions with several trainers i have come to the conclusion that the fuel oil burner should be classified the same as an induced fan furnace receiving a CAZ Depressurization limit of -15. However, High Retention Head Burners may allow this limit to go even lower. I would love an official BPI interpretation on this issue.
I have recently received a reply from Tony Peters QA for Affiliates for BPI who states that, "CAZ depressurization limits shall be identical for gas or oil fueled combustion appliances. An oil fueled combustion appliance shall not be classified as a mechanically assisted draft appliance. Please classify oil fueled combustion appliances as natural draft boilers or furnaces." He also says, "Draft calculations shall also be identical for oil or gas fueled combustion appliances. Please follow the acceptable draft test results chart found on page 10 of BA for all natural draft appliances."
Seems a bit odd to me, but he explains that, "if the oil fueled combustion appliance has been installed with a barometric damper connected to the vent pipe, it cannot support a -15Pa CAZ depressurization limit."

RSS

Home Energy Pros

Home Energy Pros was founded by the developers of Home Energy Saver Pro (sponsored by the U.S. Department of Energy,) and brought to you in partnership with Home Energy magazine.

Latest Activity

Michael Dunseith posted a status
1 hour ago
Profile IconMark Bloomfield, Effective Basement Solutions, Ricardo and 4 more joined Home Energy Pros
6 hours ago
Paul Raymer posted a blog post

Rocket Science?

The old expression when something is supposed to be simple is to say that, “This is not rocket…See More
12 hours ago
Sean Lintow Sr replied to Jim Gunshinan's discussion Tax Time Blues
"Well if I had to guess your credit will be 0 as it used to be up to $1500 & wasn't as hard…"
13 hours ago
Hannah Miller commented on Adam Flowers's blog post Comfort as a Selling Point
"Hello Adam! I hope you are still messages from this site. I just was forwarded your post and it…"
21 hours ago
Michael Dunseith replied to robert jones's discussion Should your local weatherization company be required to have someone BPI certified on their staff?
"Why the concern with airflow around heating and domestic pipes? Most are inside the envelope. What…"
yesterday
Tom White posted a video

Weatherization to Home Performance -- Tools & Tips for Developing For-profit Services

Are you a low income weatherization contractor looking to add home performance work you your services? The Home Performance Resource Center, Efficiency First, and NCAF present resources developed through expert industry engagement. While many of the…
yesterday
Jim Gunshinan posted a discussion

Tax Time Blues

There is a tax credit available to homeowners who have walls insulated. The credits were continued…See More
yesterday

© 2015   Created by Lawrence Berkeley National Laboratory.

Badges  |  Report an Issue  |  Terms of Service