Unless I have this wrong, the BPI CAZ depressurization limits and draft calculations are for gas boilers and furnaces.  Up here in New England we have a lot of oil burners.  It would seem that it would take a lot more negative pressure in a CAZ to get an oil burner to spill.  I have flue pressures for oil of: <10 F at -15 Pa, 11 - 40F at -13 Pa, 41 - 60F at -11 Pa, 61 - 90F at -9 Pa, and >90F at -7Pa.

Tags: Oil, burner, limits, pressure

Views: 321

Reply to This

Replies to This Discussion

Paul,
We see lots of fuel oil in the NC mountains where we have been training BPI for over 2.5 years now. After many discussions with several trainers i have come to the conclusion that the fuel oil burner should be classified the same as an induced fan furnace receiving a CAZ Depressurization limit of -15. However, High Retention Head Burners may allow this limit to go even lower. I would love an official BPI interpretation on this issue.
I have recently received a reply from Tony Peters QA for Affiliates for BPI who states that, "CAZ depressurization limits shall be identical for gas or oil fueled combustion appliances. An oil fueled combustion appliance shall not be classified as a mechanically assisted draft appliance. Please classify oil fueled combustion appliances as natural draft boilers or furnaces." He also says, "Draft calculations shall also be identical for oil or gas fueled combustion appliances. Please follow the acceptable draft test results chart found on page 10 of BA for all natural draft appliances."
Seems a bit odd to me, but he explains that, "if the oil fueled combustion appliance has been installed with a barometric damper connected to the vent pipe, it cannot support a -15Pa CAZ depressurization limit."

RSS

Videos

  • Add Videos
  • View All

Twitter

Latest Activity

Paul Scheckel posted a blog post

Renewable Rant: Traditional Energy!

Why, when I open up a newsletter or market evaluation report about “traditional energy” markets, do…See More
3 hours ago
Rob Madden, Solar Home Broker's discussion was featured

Indoor Air Quality Monitors and Meters

I'm considering purchasing the AirAdvice for Homes indoor air quality monitor but it seems to have…See More
4 hours ago
Luis Hernandez's discussion was featured

ERV Configuration

Greetings everyone,     I did an energy audit on this new home that is too tight and needs…See More
4 hours ago
Kim Tanner's discussion was featured
4 hours ago
John Nicholas's discussion was featured

Slab Edge Insulation - A Side Thread to Melissa's Question

Melissa Baldridge inquired about installing slab edge insulation on a potential E-Star certified…See More
4 hours ago
Melissa Baldridge's discussion was featured

ENERGY STAR - Slab Insulation

Folks,Let's say I have a client who's building slab on grade and intending to certify E-STAR.  I'm…See More
4 hours ago
Sean Maxwell's discussion was featured

Blower Door Databases: ATTMA and Retrotec rCloud

Hi guys,We're pushing for blower door testing in the building code here in Australia and we think…See More
4 hours ago
Bob Blanchette's discussion was featured

Real World Ceiling Fan CFM

Has anybody done testing on delivered CFM of ceiling fans? Energy star has a test room where the…See More
4 hours ago

© 2016   Created by Lawrence Berkeley National Laboratory.   Powered by

Badges  |  Report an Issue  |  Terms of Service