Unless I have this wrong, the BPI CAZ depressurization limits and draft calculations are for gas boilers and furnaces.  Up here in New England we have a lot of oil burners.  It would seem that it would take a lot more negative pressure in a CAZ to get an oil burner to spill.  I have flue pressures for oil of: <10 F at -15 Pa, 11 - 40F at -13 Pa, 41 - 60F at -11 Pa, 61 - 90F at -9 Pa, and >90F at -7Pa.

Tags: Oil, burner, limits, pressure

Views: 280

Reply to This

Replies to This Discussion

Paul,
We see lots of fuel oil in the NC mountains where we have been training BPI for over 2.5 years now. After many discussions with several trainers i have come to the conclusion that the fuel oil burner should be classified the same as an induced fan furnace receiving a CAZ Depressurization limit of -15. However, High Retention Head Burners may allow this limit to go even lower. I would love an official BPI interpretation on this issue.
I have recently received a reply from Tony Peters QA for Affiliates for BPI who states that, "CAZ depressurization limits shall be identical for gas or oil fueled combustion appliances. An oil fueled combustion appliance shall not be classified as a mechanically assisted draft appliance. Please classify oil fueled combustion appliances as natural draft boilers or furnaces." He also says, "Draft calculations shall also be identical for oil or gas fueled combustion appliances. Please follow the acceptable draft test results chart found on page 10 of BA for all natural draft appliances."
Seems a bit odd to me, but he explains that, "if the oil fueled combustion appliance has been installed with a barometric damper connected to the vent pipe, it cannot support a -15Pa CAZ depressurization limit."

RSS

Home Energy Pros

Home Energy Pros was founded by the developers of Home Energy Saver Pro (sponsored by the U.S. Department of Energy,) and brought to you in partnership with Home Energy magazine.

Latest Activity

Stan Kuhn replied to Mike Kandel's discussion Have you heard!? BPI's BSP Certificate Approved as Home Energy Score Prerequisite in the group Building Performance Institute (BPI)
"Mike, are there any statistics on the number of HES ratings performed, by all providers?"
2 hours ago
Mike Kandel added a discussion to the group Building Performance Institute (BPI)
Thumbnail

Have you heard!? BPI's BSP Certificate Approved as Home Energy Score Prerequisite

The Building Performance Institute's Building Science Principles (BSP) Certificate of Knowledge has…See More
2 hours ago
Mike Kandel posted a discussion

Have you heard!? BPI's BSP Certificate Approved as Home Energy Score Prerequisite!

The Building Performance Institute's Building Science Principles (BSP) Certificate of Knowledge has…See More
2 hours ago
Shawna Henderson posted a status
"New Blog Post @HomeEnergyMag Why I like Dumb, Do-Nothing Houses http://shar.es/1WSOIX"
3 hours ago
Larry Gorman posted a discussion

Hobo Data loggers for sale

I have recently retired and no longer have need of these, which are all in like new condition.  I…See More
4 hours ago
Laurel Elam posted a blog post

Over 146,000 Homes in the U.S. were HERS Rated and issued a HERS Index Score in 2014

In 2014 there were 146,860 homes in the United States that were energy rated by certified RESNET…See More
4 hours ago
Shashank Kirloskar posted a blog post

Top 8 Solar Panel Manufacturers in India

Non-Renewable resources are reducing rapidly. Powering homes and offices through other means,…See More
15 hours ago
Avi Yashchin posted a blog post
16 hours ago

© 2015   Created by Lawrence Berkeley National Laboratory.

Badges  |  Report an Issue  |  Terms of Service