Unless I have this wrong, the BPI CAZ depressurization limits and draft calculations are for gas boilers and furnaces.  Up here in New England we have a lot of oil burners.  It would seem that it would take a lot more negative pressure in a CAZ to get an oil burner to spill.  I have flue pressures for oil of: <10 F at -15 Pa, 11 - 40F at -13 Pa, 41 - 60F at -11 Pa, 61 - 90F at -9 Pa, and >90F at -7Pa.

Tags: Oil, burner, limits, pressure

Views: 299

Reply to This

Replies to This Discussion

Paul,
We see lots of fuel oil in the NC mountains where we have been training BPI for over 2.5 years now. After many discussions with several trainers i have come to the conclusion that the fuel oil burner should be classified the same as an induced fan furnace receiving a CAZ Depressurization limit of -15. However, High Retention Head Burners may allow this limit to go even lower. I would love an official BPI interpretation on this issue.
I have recently received a reply from Tony Peters QA for Affiliates for BPI who states that, "CAZ depressurization limits shall be identical for gas or oil fueled combustion appliances. An oil fueled combustion appliance shall not be classified as a mechanically assisted draft appliance. Please classify oil fueled combustion appliances as natural draft boilers or furnaces." He also says, "Draft calculations shall also be identical for oil or gas fueled combustion appliances. Please follow the acceptable draft test results chart found on page 10 of BA for all natural draft appliances."
Seems a bit odd to me, but he explains that, "if the oil fueled combustion appliance has been installed with a barometric damper connected to the vent pipe, it cannot support a -15Pa CAZ depressurization limit."

RSS

Home Energy Pros

Home Energy Pros was founded by the developers of Home Energy Saver Pro (sponsored by the U.S. Department of Energy,) and brought to you in partnership with Home Energy magazine.  Home Energy Pros is sponsored by the Better Buildings Residential Network.

Latest Activity

Benjamin Mailian replied to Kevin Eigel's discussion What is the best energy auditing software?
"This is an old post but it's still very relevant so I thought I'd give our app a mention…"
1 hour ago
Profile IconMarissaCortese, Justin Tyrrell, McHale Insulation and 1 more joined Home Energy Pros
5 hours ago
Diane Chojnowski replied to Jose Macho's discussion Google Sunroof Project- Where Are They Going with Solar?
" "
10 hours ago
Tom White's blog post was featured

Deconstructing and Moving a Historic Home

This spring in New Orleans I hosted “True Tales of Haunted Home Performance,” at the Home…See More
11 hours ago
Tom White posted a blog post

Deconstructing and Moving a Historic Home

This spring in New Orleans I hosted “True Tales of Haunted Home Performance,” at the Home…See More
14 hours ago
Kim Tanner posted a discussion

Acronym Challenge!

We challenge you to make suggestions to help troubleshoot the below problem using as many acronyms…See More
17 hours ago
Kim Tanner joined Brandon Walton's group
Thumbnail

Efficiency First Arizona Chapter

Efficiency First of Arizona is the Official State Chapter of that unites the Home Performance…See More
17 hours ago
Paul Morin commented on Sean Maxwell's blog post The Better Blower Door Test for Multifamily Energy Code
"Thanks Sean for a very will stated article.  I agree with your assessment of the importance of…"
17 hours ago

© 2015   Created by Lawrence Berkeley National Laboratory.

Badges  |  Report an Issue  |  Terms of Service