Unless I have this wrong, the BPI CAZ depressurization limits and draft calculations are for gas boilers and furnaces.  Up here in New England we have a lot of oil burners.  It would seem that it would take a lot more negative pressure in a CAZ to get an oil burner to spill.  I have flue pressures for oil of: <10 F at -15 Pa, 11 - 40F at -13 Pa, 41 - 60F at -11 Pa, 61 - 90F at -9 Pa, and >90F at -7Pa.

Tags: Oil, burner, limits, pressure

Views: 266

Reply to This

Replies to This Discussion

Paul,
We see lots of fuel oil in the NC mountains where we have been training BPI for over 2.5 years now. After many discussions with several trainers i have come to the conclusion that the fuel oil burner should be classified the same as an induced fan furnace receiving a CAZ Depressurization limit of -15. However, High Retention Head Burners may allow this limit to go even lower. I would love an official BPI interpretation on this issue.
I have recently received a reply from Tony Peters QA for Affiliates for BPI who states that, "CAZ depressurization limits shall be identical for gas or oil fueled combustion appliances. An oil fueled combustion appliance shall not be classified as a mechanically assisted draft appliance. Please classify oil fueled combustion appliances as natural draft boilers or furnaces." He also says, "Draft calculations shall also be identical for oil or gas fueled combustion appliances. Please follow the acceptable draft test results chart found on page 10 of BA for all natural draft appliances."
Seems a bit odd to me, but he explains that, "if the oil fueled combustion appliance has been installed with a barometric damper connected to the vent pipe, it cannot support a -15Pa CAZ depressurization limit."

RSS

Home Energy Pros

Home Energy Pros was founded by the developers of Home Energy Saver Pro (sponsored by the U.S. Department of Energy,) and brought to you in partnership with Home Energy magazine.

Latest Activity

Bud Poll replied to richard gaughan's discussion Advice for heating a 3-story Vermont home built in 1900?
"Hi Richard, Being a science writer and this being rental units, here is a moral dilemma you…"
1 hour ago
richard gaughan posted a discussion

Advice for heating a 3-story Vermont home built in 1900?

I'm a science writer, as opposed to an energy professional, and I joined this group to try to keep…See More
5 hours ago
Christopher Talarico posted a discussion

Heating with Tankless Water Heater & Hydronic Air Handler vs. Gas Furnace

Hi,I've looked around online and haven't found a lot of good information on home heating with…See More
16 hours ago
Profile IconSara Sabol, Christopher Talarico and Aaren Stewart joined Home Energy Pros
18 hours ago
Hal Skinner replied to Andy Gostisha's discussion Disguising Ductless Heat Pump Units
"Hi Andy. The bare metal units on a roof stick out like a sore thumb .  Coating them with our…"
18 hours ago
Paul Morin replied to Stephen Standley's discussion Which reading is more reliable on a Minneapolis Duct Blaster?
"Sorry for chiming in so late.  Sean’s comment early on in the discussion was the closest…"
21 hours ago
jerry gentile posted a status
"hello- anyone challenge the written QCI exam?"
yesterday
Kevin Jordan posted photos
yesterday

© 2014   Created by Lawrence Berkeley National Laboratory.

Badges  |  Report an Issue  |  Terms of Service