Unless I have this wrong, the BPI CAZ depressurization limits and draft calculations are for gas boilers and furnaces.  Up here in New England we have a lot of oil burners.  It would seem that it would take a lot more negative pressure in a CAZ to get an oil burner to spill.  I have flue pressures for oil of: <10 F at -15 Pa, 11 - 40F at -13 Pa, 41 - 60F at -11 Pa, 61 - 90F at -9 Pa, and >90F at -7Pa.

Tags: Oil, burner, limits, pressure

Views: 282

Reply to This

Replies to This Discussion

Paul,
We see lots of fuel oil in the NC mountains where we have been training BPI for over 2.5 years now. After many discussions with several trainers i have come to the conclusion that the fuel oil burner should be classified the same as an induced fan furnace receiving a CAZ Depressurization limit of -15. However, High Retention Head Burners may allow this limit to go even lower. I would love an official BPI interpretation on this issue.
I have recently received a reply from Tony Peters QA for Affiliates for BPI who states that, "CAZ depressurization limits shall be identical for gas or oil fueled combustion appliances. An oil fueled combustion appliance shall not be classified as a mechanically assisted draft appliance. Please classify oil fueled combustion appliances as natural draft boilers or furnaces." He also says, "Draft calculations shall also be identical for oil or gas fueled combustion appliances. Please follow the acceptable draft test results chart found on page 10 of BA for all natural draft appliances."
Seems a bit odd to me, but he explains that, "if the oil fueled combustion appliance has been installed with a barometric damper connected to the vent pipe, it cannot support a -15Pa CAZ depressurization limit."

RSS

Home Energy Pros

Home Energy Pros was founded by the developers of Home Energy Saver Pro (sponsored by the U.S. Department of Energy,) and brought to you in partnership with Home Energy magazine.

Latest Activity

Charlie Hewitt posted a blog post

Residential Electric Load Disaggregation

“What gets measured gets managed” is a quote often attributed to the venerable management expert…See More
5 hours ago
Kurt Albershardt replied to Larry Schaffert's discussion How to correctly insulate exterior wall in a 1900 house?
"Balloon framed houses make for easy upgrades IME.  We cover the open bays from the sill plate…"
5 hours ago
Kurt Albershardt replied to William Fisher's discussion Can tankless water heaters provide hot water even when the groundwater is fairly cold?
"There are a number of approaches that can work depending on the specifics of your situation. What…"
5 hours ago
Bob Mariani joined allen p tanner's group
Thumbnail

Energy Auditing Equipment for Sale, Trade or to Purchase

Discuss the pros and cons of the equipment you are interested in prior to purchase. Post equipment…See More
16 hours ago
Bob Mariani replied to William Parlapiano's discussion Equipment for Sale Updated April 9, 2015 in the group Energy Auditing Equipment for Sale, Trade or to Purchase
"I would be interested in a package deal for the items marked as "Available"  Email…"
16 hours ago
Steven Lewis replied to William Fisher's discussion Can tankless water heaters provide hot water even when the groundwater is fairly cold?
"Look at reducing the ambient humidity in the home.  The dew point is the key to the…"
Friday
Olivia Taylor posted blog posts
Friday
norman farwell replied to Bryan Pringle's discussion Dense packed cellulose in basement?
"Ha, we're on the same wavelength.  That's the big question--I'm still thinking…"
Thursday

© 2015   Created by Lawrence Berkeley National Laboratory.

Badges  |  Report an Issue  |  Terms of Service