Can blown loose insulation be used in cantilever floor?

Hi all,

Happy New Year!

Question-- can blown insulation be used in cantilever floor? Extends 3 to 6 feet. Climate: Atlanta, GA

Mom has lived in home since mid 90's and I just found this. She only this year complained of cold edge of the house in two rooms. Then I went exploring. Found 2 inch gap running length of rear of home just past sill plate. And zero insulation. The insulation under home ended at foundation wall and sill.

I covered and foamed the gap length with each joist bay. Now, can I blow in loose insulation?

Thanks!

Chris

Views: 832

Reply to This

Replies to This Discussion

Chris-----------We blow cantilevers all the time. They are prevelent in splits and second story overhangs. It sounds like you have the perfect opportunity to dense pack this area as you have already sealed the joist bays. Access sounds easy and all you will have to do is drill through your blocking and blow.

Ed Ballard

Thanks Ed. I appreciate your help. I can do nice, tight, smart A/C installs all day but insulation knowledge for me is still growing. Thanks.

Chris

Chris- you should note the difference between your term "loose" and Ed's description. Dense pack is the way to go.

How can I diy this?

Chris-----DIY may have some challenges. You will need to find a blower that has air and feed adjustments. Most box stores that have loaner equip. do not have this capibilitie. The idea of DENse pack is just that. To install the cellulose at a density that will prevent it from settling and to inhibite air flow through it. If you try an open blow into the cavity you will end up with a gap between the top of the insulation and the bottom of the subfloor. NOT GOOD.

Get on your favorite search engine and olok up dense pack cellulose insulation. It will be quicker than me trying to explain your air/feed setting. To know if you are getting in the range/pack needed push your finger into the blow . If you have trouble pushing your finger into it you are heading for bullseye.

Good luck--------just do it

Loose fill at this point will help, you have minimized the air movement with your air sealing and considering the delta T in your location you may be ok. Up where I come from it would have to be dense packed not loose filled.

 

The perferred solution is closed cell foam combined with a joist cavity  air seal R board located in line with the exterior shell sheathing. The extended joists create a building shell problem with generally heavy air leakage. The 2nd option would be dense pack cellulose either netted or packed behind R board and exterior sheathing applied over the R board or netting. Fiberglass is a poor choice in a cantilevered space particularly in colder climates as you need both a good thermal and air boundary. Again, you need to air seal/insulate the joist cavity for a good thermal shell boundary at the exterior framing sheathing.

 

I continue to find cornice crews are taught to install soffit vents at preset spacing regardless of conditions. A vented panel along a cantilevered extension can cause air infiltration in that area. We then have air/pressure into the wall section or joist cavity. In the South moisture is a concern, but I consider sealing the soffit vent so to create a true thermal barrier when insulation is installed. ....Allan

RSS

Home Energy Pros

Home Energy Pros was founded by the developers of Home Energy Saver Pro (sponsored by the U.S. Department of Energy,) and brought to you in partnership with Home Energy magazine.

Latest Activity

Christopher Morin posted a blog post

5 Things New Energy Efficiency HVAC Contractors Need to Know

1. Do not sell on Price! Use 'Simple Payback'The price of High-efficient equipment will undoubtedly…See More
3 hours ago
David Eggleton commented on David Eggleton's group Considering Permaculture &/or Transition
"In August 2014, in Minnesota, there's another unprecedented opportunity to meet and mix with a…"
10 hours ago
Glen Gallo commented on Jim Gunshinan's blog post Energy Upgrade California—Up Close and Personal
"Nate, RE: Duct test On my own home and a rental I have tested more than once over the last many…"
10 hours ago
Profile Iconangela hines and Charles Goldman joined Home Energy Pros
15 hours ago
Jeff Flaherty joined Diane Chojnowski's group
Thumbnail

Tools of the Trade

A hammer and a saw used to be the key tools for home contractors. Today, the best-in-breed also use…See More
yesterday
Jeff Flaherty joined allen p tanner's group
Thumbnail

Energy Auditing Equipment for Sale, Trade or to Purchase

Discuss the pros and cons of the equipment you are interested in prior to purchase. Post equipment…See More
yesterday
Debra Little joined David Eggleton's group
Thumbnail

Considering Permaculture &/or Transition

Some who work to increase energy efficiency and intelligent/wise use of energy are, and some will…See More
yesterday
Jim Gunshinan commented on Jim Gunshinan's blog post Energy Upgrade California—Up Close and Personal
"Thanks for all the comments. Yes, it is interesting how the duct leakage grew over the years. Maybe…"
yesterday
Ed Minch commented on Jim Gunshinan's blog post Energy Upgrade California—Up Close and Personal
"What sort of energy bill do you have now, what is  your target bill, and what will it cost to…"
yesterday
Nate Adams commented on Jim Gunshinan's blog post Energy Upgrade California—Up Close and Personal
"I look forward to hearing more about the inside of the program! The big question that came to mind…"
yesterday
Glen Gallo commented on Jim Gunshinan's blog post Energy Upgrade California—Up Close and Personal
"It is curious to see a 15% difference in the duct test from the test out of 2007 to the current…"
yesterday
John Proctor commented on Jim Gunshinan's blog post Energy Upgrade California—Up Close and Personal
"So Jim, any idea as to how your ducts sprung another 15% leakage between 2007 and 2014? You also…"
yesterday

© 2014   Created by Lawrence Berkeley National Laboratory.

Badges  |  Report an Issue  |  Terms of Service