BPI does not consider fireplaces or wood stoves to be combustion appliances.  Yet they produce CO and can backdraft fumes into a house. 


Obviously you can't perform a spillage, CO, or draft test on a fireplace, and you wouldn't want to run a blower door or duct blaster soon after having a fire in a wood stove or fireplace. 


But what do you think would be a good worst case depressurization limit for a fireplace or wood stove?  -5 pascals, same as a natural drafting furnace or boiler?


Anyone ever do a spillage, CO, or draft test on a wood stove?


What have you done or recommended if a fireplace or wood stove backdrafts under worst case or natural conditions?




Tags: Backdrafting, CAZ, depressurization

Views: 614

Reply to This

Replies to This Discussion

I think a WCD of -5pa is pretty reasonable, but like Adam I would love to see some data!
The guys at the energy conservatory did some work on this a number of years ago. As I recall, 6 Pascals is enough to backdraft an operational fireplace. BPI does consider fireplaces and woodstoves CAZs.
Couple of things, though. 1. The worst part of a fireplace fire is at the end of the burn, when the chimney is cooling, and combustion is incomplete. Those romantic embers can be deadly. If a fireplace or woodstove backdrafts at the beginning, people usually don't like the smoke and open a window, which may or may not help.
2. I think you have to consider a fireplace or woodstove as a serious participant in sucking the air out of the house for worst case depressurization. I use the blower door to draw 250 to 300 cfm out of the house along with all the other exhaust appliances. No, I don't start a fire and see what happens!
Wow that is interesting, running the blower door at 250 to 300 cfm to simulate what the real worst case would be like with a fire in the fireplace or wood stove.

BPI may consider fireplaces and wood stoves to be CAZs, but they don't have any depressurization limits or action levels to implement for them. So as far as BPI goes, you could have a house with a worst case depressurization of -10 pascals and a fireplace or wood stove, and it would pass with flying colors with no requirements or recommendations to fix anything.


Home Energy Pros

Home Energy Pros was founded by the developers of Home Energy Saver Pro (sponsored by the U.S. Department of Energy,) and brought to you in partnership with Home Energy magazine.  Home Energy Pros is sponsored by the Better Buildings Residential Network.

Latest Activity

Grzegorz is now a member of Home Energy Pros
2 hours ago
Rod Fox replied to Rod Fox's discussion Utility Meter Accuracy
"Dennis, that's a ton of useful info and it will take me a bit to fully assimilate those…"
3 hours ago
Ben Haas replied to Rod Fox's discussion Utility Meter Accuracy
"Yup..... 1200 amp service to the compound.....  3 -400 amp panels, all single phase since 3…"
15 hours ago
Walter Ahlgrim replied to Rod Fox's discussion Utility Meter Accuracy
"The more I think about it if the problem cannot be the current transformers reading small loads,…"
20 hours ago
Dennis Heidner replied to Rod Fox's discussion Utility Meter Accuracy
"Note to readers 0.5A instead of 5A for reading with A/D.... the edit to correct that didn't…"
21 hours ago
Dennis Heidner replied to Rod Fox's discussion Utility Meter Accuracy
"Rod, I have some of the CT's that you referenced in the openenergymonitor system.  They…"
21 hours ago
Tauran Ivall replied to Tauran Ivall's discussion Energy Efficient Entry Door options out there?
"Graham, How did this Plasproinc door cost?  Do you have any photos you can share a link to?"
21 hours ago
Dennis Heidner replied to Rod Fox's discussion Utility Meter Accuracy
"1200A service... really?  or did you mean 200A.  That size service would likely result in…"
22 hours ago

© 2015   Created by Lawrence Berkeley National Laboratory.   Powered by

Badges  |  Report an Issue  |  Terms of Service