BPI does not consider fireplaces or wood stoves to be combustion appliances.  Yet they produce CO and can backdraft fumes into a house. 

 

Obviously you can't perform a spillage, CO, or draft test on a fireplace, and you wouldn't want to run a blower door or duct blaster soon after having a fire in a wood stove or fireplace. 

 

But what do you think would be a good worst case depressurization limit for a fireplace or wood stove?  -5 pascals, same as a natural drafting furnace or boiler?

 

Anyone ever do a spillage, CO, or draft test on a wood stove?

 

What have you done or recommended if a fireplace or wood stove backdrafts under worst case or natural conditions?

 

 

 

Tags: Backdrafting, CAZ, depressurization

Views: 598

Reply to This

Replies to This Discussion

I think a WCD of -5pa is pretty reasonable, but like Adam I would love to see some data!
The guys at the energy conservatory did some work on this a number of years ago. As I recall, 6 Pascals is enough to backdraft an operational fireplace. BPI does consider fireplaces and woodstoves CAZs.
Couple of things, though. 1. The worst part of a fireplace fire is at the end of the burn, when the chimney is cooling, and combustion is incomplete. Those romantic embers can be deadly. If a fireplace or woodstove backdrafts at the beginning, people usually don't like the smoke and open a window, which may or may not help.
2. I think you have to consider a fireplace or woodstove as a serious participant in sucking the air out of the house for worst case depressurization. I use the blower door to draw 250 to 300 cfm out of the house along with all the other exhaust appliances. No, I don't start a fire and see what happens!
Wow that is interesting, running the blower door at 250 to 300 cfm to simulate what the real worst case would be like with a fire in the fireplace or wood stove.

BPI may consider fireplaces and wood stoves to be CAZs, but they don't have any depressurization limits or action levels to implement for them. So as far as BPI goes, you could have a house with a worst case depressurization of -10 pascals and a fireplace or wood stove, and it would pass with flying colors with no requirements or recommendations to fix anything.

RSS

Home Energy Pros

Home Energy Pros was founded by the developers of Home Energy Saver Pro (sponsored by the U.S. Department of Energy,) and brought to you in partnership with Home Energy magazine.  Home Energy Pros is sponsored by the Better Buildings Residential Network.

Latest Activity

Profile IconBenney Dornevil, Mike Norvell Sr and Jen Loomis joined Home Energy Pros
yesterday
Joanie Minor posted a status
"Home Performance Institute now offers OSHA 10 and Confined Space Classes. Call 203-536-2151 to register."
yesterday
Joanie Minor posted a photo
yesterday
John Kaye posted a blog post

FREE Home Efficiency & Safety Assessments in the Los Angeles County area.

Since last June I have been qualifying homeowners in the Los Angeles County for the Home Upgrade…See More
yesterday
Eric Kjelshus replied to Rod Fox's discussion Does calcification affect electric water heater aquastat temperature sensor performance?
"Those 240 Volt aquastats shut off and then on kinda quick back on.  The older the tank the…"
yesterday
Rod Fox replied to Rod Fox's discussion Does calcification affect electric water heater aquastat temperature sensor performance?
"Well I'd love to tell you folks I found an answer, but I did not... I went to my…"
yesterday
Rod Fox replied to Kevin Eigel's discussion What is the best energy auditing software?
"I've been trying to answer this question for many years and have not yet found an answer.…"
yesterday
Jerry Lawrence posted events
yesterday

© 2015   Created by Lawrence Berkeley National Laboratory.

Badges  |  Report an Issue  |  Terms of Service