http://homeenergypros.lbl.gov/video/ashrae-62-2-2013-easy-peasy-ven...

Here you go, dudes:

7.5 cfm per person + 3 cfm per 100 sq. ft. CFA
MINUS
[ 1000 x ELA x (H/8.2)ˆ0.4 x WSF ] / 7.3

Tags: 62.2, 62.2-2013, ashrae, calculation, sizing, ventilation

Views: 300

Reply to This

Replies to This Discussion

Corbett, where were you when I was struggling through math in high school and college? Videos like this would have come in handy!

Thanks, Corbett. Another successfully simple and succinct explanation. Good work.