Are Zoned Heating/Cooling Systems a Good Idea or a Bad Idea?

For starters, I live in Atlanta, Ga and I am not an HVAC pro so this is a serious question that I would like answered for one of my clients.  I understand the premise of a zoned system and on the surface, it sounds like a good idea. Then I considered the fact that I have always told my customers that it is a bad idea to close off vents in rooms they are not in because of duct leakage.  Also, the second law of thermodynamics simply states the hot goes to cold, so now the unheated areas are doing their best to rob warm air from the heated areas.  Finally, if your zoning a single system, aren't you creating on oversizing issue because the unit (that was probably oversized in the first place) is now servicing a smaller are than what it was designed for?

 

I look forward to your input.

Views: 1749

Reply to This

Replies to This Discussion

Some of the benefit to 2 stage A/C units is the "oversized coils" in relation to compressor size when the unit is operating on low stage. If a 2 stager unit is 2ton/3ton you have a 2ton A/C system most of the time with 3 ton sized condenser and evaporator coils. More coil surface area = better heat transfer.

I wanted to add, that a furnace or boiler that can modulate has a far greater means of tailoring capacity to load. A 5:1 modulating range or turndown range, is excellent and your 60 MBH appliance can work very well, if not more efficiently at 12 MBH input (10.8 MBH output or more), given the larger internal surface areas.

So the "it depends" part of the answer hinges a lot on what kind of appliance you have. Single stage? Not so much. :)
Hi Jon- Yes, I figured you were forced hot air and AC, but I used the HW example as to how one can mitigate the cycling issue. Also the contrast between FHA/AC and hydronic systems.
Those examples aside, the principles still hold- if your system modulates capacity, you stand a higher chance of maintaining efficiency.

Also, on the cooling side, you already know that you cannot drop your airflow below critical levels or you will freeze-over your coil. Most AC-based zoning systems, I call them 30/70 systems because they apportion all of the airflow/capacity to those approximate portions per zone. The system still puts out 100% but is directed to greatest need. These systems frequently are appropriately under-sized (say what is a 4.5 to 5 ton system on paper, might be sized at 3.5 to 4 tons based on the most likely concurrent load and not the sum of peak loads, which will never really occur.)

To modulate refrigerant capacity, the newer inverter driven compressors are outstanding, but are not widely available outside of the so-called ductless split systems, but should be available across conventional split systems in the next year or so. Until then, multi-stage seems to be the best one can do. A Rawal APR valve has great utility in modulating refrigerant flow especially in single-stage systems. A lot of good options out there.

On the combustion side, gas modulations is your only choice and the deeper the better.

Brad

Thanks for the info Brad, it was very helpful.  What actually got me to ask this question came from a recent client that spent a bunch of money adding zoning to an existing system.  Oversizing is a common issue here because no one did manual J's because there were very few building codes (and even fewer enforced) during the 90's building boom.  This guys actual reason for doing the zoning was due to serious comfort issues in a large bonus room over the garage.  He was talked into zoning by a HVAC contractor.  During my audit, I found ducts running to that area that were disconnected and the rest were not properly sealed so that contractor never even inspected the condition of the current system.  The homeowner has used the zoning and weatherstripping on the door to completely shut off that room and they only use it when they have company (sad but true).  This has now created other issues.  Basically, the homeowner wasted a bunch of money and is now reluctant to spend more money to actually fix his problems.

I will definitely keep your info for future reference.

 

Thanks

You are welcome, Jon.
Man, that hurts, when a client has gone down a counter-productive path. Unfortunately, a lot of well-meaning efforts turn sour in hindsight; everyone has their expertise and the big picture is lost.

What I have found is sometimes necessary is to "recombine" the zones into one large one. This means opening doors too, not only to share the conditions, but also that return air paths are rarely effective nor predictable.

If you do have a short-cycling issue on the cooling side, check out the Rawal APR device I mentioned. They run about $500-600 plus installation and requires a pull and recharge on the refrigerant side. But they can take a 3.5 ton unit down to 1.5 tons as a "top of the head" example. This means long, low, steady operation and the goal in your area -dehumidification.

Good luck!

Brad

2 floors should have 2 separate systems in most cases. It just makes more sense because it reduces ductwork lengths and system complexity. If one system fails the occupants can resided in the other part of the house until they can get the broke system serviced.

Our house is a single story and I have "redneck zone control" installed. It amounts to a damper in the attic that I manually adjust for summer or winter since we like having the master bedroom cooler than the rest of the house. Simple, low cost, and effective.

RSS

Home Energy Pros

Home Energy Pros was founded by the developers of Home Energy Saver Pro (sponsored by the U.S. Department of Energy, under the American Recovery and Reinvestment Act) and brought to you in partnership with Home Energy magazine.

Latest Activity

Dennis Heidner replied to J.C. Martel's discussion Disasters & sustainable energy
"Mark,  I am quite sure that if the Seattle grid were to go down - the Bullitt Center building…"
1 hour ago
Mark Richardson added a discussion to the group Renewable Energy
Thumbnail

Disasters & sustainable energy

Read my response to J.C. Martel's discussion:…See More
17 hours ago
Mark Richardson replied to J.C. Martel's discussion Disasters & sustainable energy
"Hi All, Interesting topic - myriad issues in play here, but I’ll try to touch on the ones I…"
17 hours ago
Eric Kjelshus replied to Johnny Ritzo's discussion Selecting a Water Heater
"I have been using  Rheem or State or Brad/white PVC flued tank type hot water heater…"
yesterday
Bachi Brunato replied to Bachi Brunato's discussion Boxing and Insulating Around Non-ICAT Cans
"As it turns out, we have 10 Halo 99RT housings with Halo 998P Eyeball trim in the kitchen. The trim…"
yesterday
Bachi Brunato's discussion was featured

Boxing and Insulating Around Non-ICAT Cans

I have a client with 16) 4" halogen recessed light fixtures in the attic.I'd like to cover the cans…See More
yesterday
Johnny Ritzo's discussion was featured

Selecting a Water Heater

I am looking at updating the heating and water heating systems in a rental home I recently…See More
yesterday
George Kopf's discussion was featured

Misting Aeroseal in Pressurized Home = Amazing Air Sealing Innovation

As a training program manager for a non-profit, I am often too busy managing my program to catch…See More
yesterday
Tom Delconte's blog post was featured
yesterday
Christopher Morin's blog post was featured

Selling with Rebates: The Simple Payback

  The easiest way to show a homeowner how their investment in high-efficient equipment will help…See More
yesterday
Edward Foskey's blog post was featured
yesterday
Mike Rogers's blog post was featured

HOMES Act introduced with Bi-Partisan Sponsorship

We don't see a lot of bi-partisan bills in Congress these days. Here's one focusing on home…See More
yesterday

© 2013   Created by Lawrence Berkeley National Laboratory.

Badges  |  Report an Issue  |  Terms of Service