Tags:
Permalink Reply by Bob Blanchette on December 29, 2012 at 2:19pm Overheating of the 2nd floor/Over-cooling the 1st floor is a valid concern with a zoned or 2 separate systems. The systems could be designed to "swap returns", the upstairs system gets it's return air from downstairs and downstairs gets return from upstairs. With the "swapped returns" it may be possible not to have ANY A/C required for the downstairs IF the returns were strategically located. The same could hold true for the upstairs, getting all of it's heat from downstairs.
The issue with "swapping returns" is in summer you want the return at the hottest point which is in the ceiling of the top floor and in winter you want to pull the cold air near the floor of the downstairs.
Home Energy Pros was founded by the developers of Home Energy Saver Pro (sponsored by the U.S. Department of Energy, under the American Recovery and Reinvestment Act) and brought to you in partnership with Home Energy magazine.
Joe Huang posted a discussion
Tom Delconte commented on Tom Delconte's blog post Lykans $29, Vampires $0 !
Joseph Lamy commented on Jim Gunshinan's blog post The Universe Is Made of Stories
J.C. Martel replied to J.C. Martel's discussion Disasters & sustainable energy
Judi Lyall joined allen p tanner's group
Judi Lyall replied to David Starrett's discussion I am looking for a good IR camera in the group Energy Auditing Equipment for Sale, Trade or to Purchase
Tom Maides commented on Jim Gunshinan's blog post The Universe Is Made of Stories© 2013 Created by Lawrence Berkeley National Laboratory.