Greetings everyone!

    I have a technical questions I hope I could get some feedback! I understood that air source heat pumps are very efficient because of their ductless configuration. I have been told by a very smart person that adding a duct to a airsource heat pump (Daikin has now a unit that comes with duct) does not diminish with any great significance the efficiency of the unit.  

   I of course have my reasons to believe that using ducts is increasing the liability to the system, but I like to refrain my reasons so I do not "influence" your thoughts...   

   Your thoughts?, which systems would you prefer? There are two working situations for this conversation, one is a 60 x 40 open floor, one room building (no kitchen, and no bathroom -just a working space); the other one is a 3 bedroom system home about 2500sq (both units are going to be air sealed and properly insulated. 

   Thank you everyone! 

Luis

Tags: air, duct, ductless, efficiency, heat, minisplits, pump, source

Views: 265

Reply to This

Replies to This Discussion

Equipment is rated for it's configuration (ducted or ductless). So you can compare equipment efficiencies directly. However, a ductless system has no distribution losses. A ducted system would have losses if the ducts are in unconditioned space. A ducted system will also have higher fan energy.

Now does a ducted minisplit has the same efficiency as a ductless? Yes & No. If it's a single indoor head & single outdoor condenser, Yes. But if it's a multi indoor head set up with 1 outdoor unit, there is usually an efficiency drop (rated).

RSS

Featured Forum Discussions

What causes a temperature plane in a home

Started by Energy Wise Solutions in HVAC. Last reply by Peter Krych yesterday. 4 Replies

Velocity Pressure Testing

Started by Horace Douglas Hunt, Jr. in General Forum. Last reply by Horace Douglas Hunt, Jr. Apr 15. 2 Replies

Videos

  • Add Videos
  • View All

Latest Activity

Crosbey Archery posted a blog post
3 hours ago
Profile IconRon Sarrick and Alana Barnett joined Home Energy Pros
15 hours ago
Jim Fowler posted a discussion

TREAT modeling of mid-rise apartments low heating load

Does anyone have experience using TREAT to model mid-rise (3-story) apartment buildings with…See More
yesterday
Peter Krych replied to Energy Wise Solutions's discussion What causes a temperature plane in a home
"I also should have asked where the furnace was located,basement,1st or 2nd floor. In any case the…"
yesterday
Profile IconJim Fowler, Jennifer Flanagan, Debra Smit and 2 more joined Home Energy Pros
yesterday
Eric Sperline added a discussion to the group Energy Auditing Equipment for Sale, Trade or to Purchase
Thumbnail

Wanted: Energy Auditing Equipment for sale

I am looking to buy a door frame panel that will accept a duct blaster fan.  I don't need the…See More
Friday
Energy Wise Solutions replied to Energy Wise Solutions's discussion What causes a temperature plane in a home
"This scenario occurs in the Winter Months.  It is warmer upstairs.  This is a forced Air…"
Friday
Peter Krych replied to Energy Wise Solutions's discussion What causes a temperature plane in a home
"Are these winter conditions, is it colder or warmer upstairs, is it forced air or radiant heat? It…"
Thursday

Home Energy Pros

Welcome to Home Energy Pros – the unique digital community by and for those who work in the home energy performance arena.

Home Energy Pros was founded by the developers of Home Energy Saver Pro (supported by the U.S. Department of Energy) and brought to you in partnership with Home Energy magazine.  Home Energy Pros is sponsored by the Better Buildings Residential Network. Please honor our Guidelines

© 2017   Created by Lawrence Berkeley National Laboratory.   Powered by

Badges  |  Report an Issue  |  Terms of Service