Greetings everyone!

    I have a technical questions I hope I could get some feedback! I understood that air source heat pumps are very efficient because of their ductless configuration. I have been told by a very smart person that adding a duct to a airsource heat pump (Daikin has now a unit that comes with duct) does not diminish with any great significance the efficiency of the unit.  

   I of course have my reasons to believe that using ducts is increasing the liability to the system, but I like to refrain my reasons so I do not "influence" your thoughts...   

   Your thoughts?, which systems would you prefer? There are two working situations for this conversation, one is a 60 x 40 open floor, one room building (no kitchen, and no bathroom -just a working space); the other one is a 3 bedroom system home about 2500sq (both units are going to be air sealed and properly insulated. 

   Thank you everyone! 

Luis

Tags: air, duct, ductless, efficiency, heat, minisplits, pump, source

Views: 237

Reply to This

Replies to This Discussion

Equipment is rated for it's configuration (ducted or ductless). So you can compare equipment efficiencies directly. However, a ductless system has no distribution losses. A ducted system would have losses if the ducts are in unconditioned space. A ducted system will also have higher fan energy.

Now does a ducted minisplit has the same efficiency as a ductless? Yes & No. If it's a single indoor head & single outdoor condenser, Yes. But if it's a multi indoor head set up with 1 outdoor unit, there is usually an efficiency drop (rated).

RSS

Home Energy Pros

Home Energy Pros was founded by the developers of Home Energy Saver Pro (sponsored by the U.S. Department of Energy,) and brought to you in partnership with Home Energy magazine.  Home Energy Pros is sponsored by the Better Buildings Residential Network.

Latest Activity

Kim Tanner posted videos
54 minutes ago
Don Fitchett posted a blog post
20 hours ago
Benny hani replied to Benny hani's discussion Software
"Thank you so much for your help."
21 hours ago
Sean Lintow Sr replied to Benny hani's discussion Software
"At minimum a personal CO detector, 1 blower door, 1 duct tester, 2 manometers - other equipment…"
yesterday
Greg Hannah posted a blog post
yesterday
Richardson Fred posted a discussion
yesterday
Benny hani replied to Benny hani's discussion Software
"Hello Sean I am about to purchase the equiptments needed to Start my business. I am going to be…"
yesterday
romeo traian replied to w d's discussion AERC testing and Solar Grates update
"w d, i visited your site... interesting... could you please say something more... re the…"
yesterday

© 2015   Created by Lawrence Berkeley National Laboratory.

Badges  |  Report an Issue  |  Terms of Service