Greetings everyone!

    I have a technical questions I hope I could get some feedback! I understood that air source heat pumps are very efficient because of their ductless configuration. I have been told by a very smart person that adding a duct to a airsource heat pump (Daikin has now a unit that comes with duct) does not diminish with any great significance the efficiency of the unit.  

   I of course have my reasons to believe that using ducts is increasing the liability to the system, but I like to refrain my reasons so I do not "influence" your thoughts...   

   Your thoughts?, which systems would you prefer? There are two working situations for this conversation, one is a 60 x 40 open floor, one room building (no kitchen, and no bathroom -just a working space); the other one is a 3 bedroom system home about 2500sq (both units are going to be air sealed and properly insulated. 

   Thank you everyone! 

Luis

Tags: air, duct, ductless, efficiency, heat, minisplits, pump, source

Views: 229

Reply to This

Replies to This Discussion

Equipment is rated for it's configuration (ducted or ductless). So you can compare equipment efficiencies directly. However, a ductless system has no distribution losses. A ducted system would have losses if the ducts are in unconditioned space. A ducted system will also have higher fan energy.

Now does a ducted minisplit has the same efficiency as a ductless? Yes & No. If it's a single indoor head & single outdoor condenser, Yes. But if it's a multi indoor head set up with 1 outdoor unit, there is usually an efficiency drop (rated).

RSS

Home Energy Pros

Home Energy Pros was founded by the developers of Home Energy Saver Pro (sponsored by the U.S. Department of Energy,) and brought to you in partnership with Home Energy magazine.  Home Energy Pros is sponsored by the Better Buildings Residential Network.

Latest Activity

Rick Karg replied to Carly@AirCycler's discussion The (Small) Cost of Ventilation Without Recovery
"As a member of the ASHRAE 62.2 committee (and president of Residential Energy Dynamics, the author…"
19 hours ago
Bradford E. White replied to Elizabeth Guinn's discussion ERV in need of backflow preventer.
"I would use an in-line backdraft damper such as Artis Industries or the ones made by Fantech and…"
yesterday
Kim Tanner posted a video

Wireless Air Leakage Testing

This webinar will discuss the use of WiFi technology to conduct and document blower door and duct leakage tests for compliance with local energy codes. The s...
yesterday
Profile IconPerry Grossman, Daniel Pate and Ottawa Furnace Filters joined Home Energy Pros
yesterday
Kirsten Richnavsky added a discussion to the group Building Performance Institute (BPI)
Thumbnail

Breaking the link between unhealthy homes and unhealthy kids

Listen in on IAQ Radio to a discussion on reducing the household triggers that cause asthmaattacks…See More
yesterday
Kirsten Richnavsky posted a discussion

Breaking the link between unhealthy homes and unhealthy kids

Listen in on IAQ Radio to a discussion on reducing the household triggers that cause asthmaattacks…See More
yesterday
Kim Tanner posted events
yesterday
Ottawa Furnace Filters posted a blog post

Some Useful Information about Furnace Air Filters

There is not much we can do about the air pollution outside of a house in Ottawa, Canada, but we…See More
yesterday

© 2015   Created by Lawrence Berkeley National Laboratory.

Badges  |  Report an Issue  |  Terms of Service