Can anyone share their experience with air sampling of low pressure 2 part foam in residential homes? I'm about 20 hours into reading endless amounts of information relating to the hazards and need help  Anybody had any experience with OSHA or PELS of typical retrofits?

Views: 305

Reply to This

Replies to This Discussion

Cory, we have tried badges to detect airborne isocyanates.  The ones we tried were not sufficiently sensitive to detect the components in the low pressure foam we were using.

 

We also have talked with our foam manufacturer and with our respirator cartridge supplier.  We concluded that the best way to minimize the risks of long term exposure is to use positive pressure, outdoor supplied air respirators rather than the dual cartridge respirators.  Also, good engineering controls (lots of ventilation) should be used during the foam application.

 

Homeowners definitely need to be out of the house during application and for the manufacturer's recommended period afterwards.  We also recommend that pets be out of the house.  Installers need to be protected from exposure during this period as well.

Thanks Jon, we do all of the above with the exception of the homeownerns leaving. They are denied access to where the foam is being applied and we ventilate.

 

 

As a manufacturer of low pressure SPF, Fomo has done multiple air monitoring studies.  Our Product Stewardship Guidelines outline a typical air monitoring study done in Connecticut. I have tried to attach this, but it can also be found at www.fomo.com.  You can see on page 9 that the concentrations detected were well below OSHA limits.  It's great that you are ventilating and wearing the proper PPE, however, we would agree with Jon that the occupants should vacate during the work and with Handi-Foam SPF for one hour after you have stopped spraying, this typically gives you enough time to clean-up and the homeowner can be back home. 

Attachments:

InsulSmart is a two-part aminoplast interior foam insulation offered by cfiFOAM, Inc. based in Knoxville, TN. InsulSmart - when tested per ASTM D-5116 @ "full chamber"-  showed low emissions rapidly declining from 24.6 ppb @ 7-days, to 6.5 ppb @ 14-days,  to 0.8 ppb @ 21-days, and to less than 0.8 ppb @ 28-days, which is pretty close to zero emissions. The product's low emissions reflect 1) processing to remove virtually all free-formaldehyde prior to packaging; 2) sophisticated cross-linking chemistry that reduces formaldehyde emissions to levels below ambient in many instances.

A report of ASTM D-5116 is attached along with a summary of various federal agency's guidelines. For product information and to view a short video clip, go to www.cfifoam.com.

Attachments:

RSS

Home Energy Pros

Home Energy Pros was founded by the developers of Home Energy Saver Pro (sponsored by the U.S. Department of Energy,) and brought to you in partnership with Home Energy magazine.  Home Energy Pros is sponsored by the Better Buildings Residential Network.

Latest Activity

Richard C. MacCrea replied to Damien Greenfield's discussion Is there is cost saving for you in having a tankless water heater?
"Most of the posts here are far too narrow in scope. To make the best decision you need to…"
13 hours ago
Tom Mallard replied to Damien Greenfield's discussion Is there is cost saving for you in having a tankless water heater?
"Thx, Jose, add in u"
15 hours ago
tedkidd replied to Damien Greenfield's discussion Is there is cost saving for you in having a tankless water heater?
"Thankless water heaters are a GREAT deal.... For the installers. They are usually very…"
16 hours ago
Jose Carreno replied to Damien Greenfield's discussion Is there is cost saving for you in having a tankless water heater?
"I have been working with RUUD/RHEEM tank less water heaters (0.94 energy factor) with excellent…"
18 hours ago
Profile IconColleen Neel, Sarah Mostafa, Michael Kelemen and 4 more joined Home Energy Pros
19 hours ago
David I. Shepherd-Gaw replied to Ryan Miller's discussion Wouldn't it make more sense to post jobs on a single board nationally? in the group Job Board
"I have managed and overseen several efforts with www.energyexpert.org and other similar sites. It…"
20 hours ago
David Baerg replied to Bachi Brunato's discussion Modeling a Gas Fireplace in Wrightsoft
"I would not include it.  Given that it is likely much less efficient than the gas furnace, you…"
22 hours ago
Ryan Miller posted a discussion

First NC and now GA - Building Performance Associations taking shape

Hi All - Just a quick "this is what we're up to" for the community.The NC Building Performance…See More
22 hours ago

© 2015   Created by Lawrence Berkeley National Laboratory.

Badges  |  Report an Issue  |  Terms of Service