Can anyone share their experience with air sampling of low pressure 2 part foam in residential homes? I'm about 20 hours into reading endless amounts of information relating to the hazards and need help  Anybody had any experience with OSHA or PELS of typical retrofits?

Views: 341

Reply to This

Replies to This Discussion

Cory, we have tried badges to detect airborne isocyanates.  The ones we tried were not sufficiently sensitive to detect the components in the low pressure foam we were using.

 

We also have talked with our foam manufacturer and with our respirator cartridge supplier.  We concluded that the best way to minimize the risks of long term exposure is to use positive pressure, outdoor supplied air respirators rather than the dual cartridge respirators.  Also, good engineering controls (lots of ventilation) should be used during the foam application.

 

Homeowners definitely need to be out of the house during application and for the manufacturer's recommended period afterwards.  We also recommend that pets be out of the house.  Installers need to be protected from exposure during this period as well.

Thanks Jon, we do all of the above with the exception of the homeownerns leaving. They are denied access to where the foam is being applied and we ventilate.

 

 

As a manufacturer of low pressure SPF, Fomo has done multiple air monitoring studies.  Our Product Stewardship Guidelines outline a typical air monitoring study done in Connecticut. I have tried to attach this, but it can also be found at www.fomo.com.  You can see on page 9 that the concentrations detected were well below OSHA limits.  It's great that you are ventilating and wearing the proper PPE, however, we would agree with Jon that the occupants should vacate during the work and with Handi-Foam SPF for one hour after you have stopped spraying, this typically gives you enough time to clean-up and the homeowner can be back home. 

Attachments:

InsulSmart is a two-part aminoplast interior foam insulation offered by cfiFOAM, Inc. based in Knoxville, TN. InsulSmart - when tested per ASTM D-5116 @ "full chamber"-  showed low emissions rapidly declining from 24.6 ppb @ 7-days, to 6.5 ppb @ 14-days,  to 0.8 ppb @ 21-days, and to less than 0.8 ppb @ 28-days, which is pretty close to zero emissions. The product's low emissions reflect 1) processing to remove virtually all free-formaldehyde prior to packaging; 2) sophisticated cross-linking chemistry that reduces formaldehyde emissions to levels below ambient in many instances.

A report of ASTM D-5116 is attached along with a summary of various federal agency's guidelines. For product information and to view a short video clip, go to www.cfifoam.com.

Attachments:

RSS

Featured Forum Discussions

Too many BTU's. Too much horsepower?

Started by Steve in General Forum. Last reply by Eric Kjelshus on Saturday. 4 Replies

Stack/wind pressure and flow networks.

Started by Daniel James Grundy in Training. Last reply by Daniel James Grundy Mar 23. 5 Replies

BDT with vermiculite in hollow CMU walls?

Started by Brad Cook in General Forum. Last reply by John Nicholas Mar 23. 2 Replies

Videos

  • Add Videos
  • View All

Latest Activity

Chris Dorsi commented on Home Energy Magazine's blog post The Elephant in the Room
"This was a great session, witness the fact that we had to schedule a second showing to accommodate…"
8 hours ago
Chris Dorsi liked Home Energy Magazine's blog post The Elephant in the Room
8 hours ago
eric anderson added a discussion to the group Energy Auditing Equipment for Sale, Trade or to Purchase
Thumbnail

Equipement still for sail (what is left from what I was selling before)

For some reason I can't reply to my previous thread.  I sold the blower door and duct blaster/flow…See More
15 hours ago
Mark Sackerson replied to angela stanzione's discussion Used Weatherization and auditing equipment for sale in the group Energy Auditing Equipment for Sale, Trade or to Purchase
"Angela, Do you have any blower door sets left? mark"
16 hours ago
Mark Sackerson replied to Jeffrey Anthony's discussion Blower Door Kits in the group Energy Auditing Equipment for Sale, Trade or to Purchase
"Jeffrey, do you have any blower door kits left? mark msackerson@franzoso.com"
16 hours ago
Mark Sackerson joined allen p tanner's group
Thumbnail

Energy Auditing Equipment for Sale, Trade or to Purchase

Discuss the pros and cons of the equipment you are interested in prior to purchase. Post equipment…See More
16 hours ago
Profile IconMark Sackerson and Matt Ward joined Home Energy Pros
16 hours ago
Quinn Korzeniecki's discussion was featured

Join BPI's New Professional Website Focus Group

Want to be part of the elite group of individuals that views the new BPI professional website…See More
16 hours ago

Home Energy Pros

Welcome to Home Energy Pros – the unique digital community by and for those who work in the home energy performance arena.

Home Energy Pros was founded by the developers of Home Energy Saver Pro (supported by the U.S. Department of Energy) and brought to you in partnership with Home Energy magazine.  Home Energy Pros is sponsored by the Better Buildings Residential Network. Please honor our Guidelines

© 2017   Created by Lawrence Berkeley National Laboratory.   Powered by

Badges  |  Report an Issue  |  Terms of Service