Can anyone share their experience with air sampling of low pressure 2 part foam in residential homes? I'm about 20 hours into reading endless amounts of information relating to the hazards and need help  Anybody had any experience with OSHA or PELS of typical retrofits?

Views: 309

Reply to This

Replies to This Discussion

Cory, we have tried badges to detect airborne isocyanates.  The ones we tried were not sufficiently sensitive to detect the components in the low pressure foam we were using.


We also have talked with our foam manufacturer and with our respirator cartridge supplier.  We concluded that the best way to minimize the risks of long term exposure is to use positive pressure, outdoor supplied air respirators rather than the dual cartridge respirators.  Also, good engineering controls (lots of ventilation) should be used during the foam application.


Homeowners definitely need to be out of the house during application and for the manufacturer's recommended period afterwards.  We also recommend that pets be out of the house.  Installers need to be protected from exposure during this period as well.

Thanks Jon, we do all of the above with the exception of the homeownerns leaving. They are denied access to where the foam is being applied and we ventilate.



As a manufacturer of low pressure SPF, Fomo has done multiple air monitoring studies.  Our Product Stewardship Guidelines outline a typical air monitoring study done in Connecticut. I have tried to attach this, but it can also be found at  You can see on page 9 that the concentrations detected were well below OSHA limits.  It's great that you are ventilating and wearing the proper PPE, however, we would agree with Jon that the occupants should vacate during the work and with Handi-Foam SPF for one hour after you have stopped spraying, this typically gives you enough time to clean-up and the homeowner can be back home. 


InsulSmart is a two-part aminoplast interior foam insulation offered by cfiFOAM, Inc. based in Knoxville, TN. InsulSmart - when tested per ASTM D-5116 @ "full chamber"-  showed low emissions rapidly declining from 24.6 ppb @ 7-days, to 6.5 ppb @ 14-days,  to 0.8 ppb @ 21-days, and to less than 0.8 ppb @ 28-days, which is pretty close to zero emissions. The product's low emissions reflect 1) processing to remove virtually all free-formaldehyde prior to packaging; 2) sophisticated cross-linking chemistry that reduces formaldehyde emissions to levels below ambient in many instances.

A report of ASTM D-5116 is attached along with a summary of various federal agency's guidelines. For product information and to view a short video clip, go to



Home Energy Pros

Home Energy Pros was founded by the developers of Home Energy Saver Pro (sponsored by the U.S. Department of Energy,) and brought to you in partnership with Home Energy magazine.  Home Energy Pros is sponsored by the Better Buildings Residential Network.

Latest Activity

Walter Ahlgrim replied to Rod Fox's discussion Utility Meter Accuracy
"The problem is this metering type of system cannot be accurate if the load is less than 20% of the…"
1 hour ago
Dennis Heidner replied to Rod Fox's discussion Utility Meter Accuracy
"yes,  I'd think even for a very large house / residence that you'd want to look…"
1 hour ago
Bob Blanchette replied to Rod Fox's discussion Utility Meter Accuracy
"50KW is REALLY pushing it on a standard residential meter, that's 208A @ 240v. $873 minimum…"
4 hours ago
Dennis Heidner replied to Rod Fox's discussion Utility Meter Accuracy
"Yup,  but it also looks like for the tariffs above residential services that they include…"
9 hours ago
Dan McKee posted a blog post

9 Tips To Get Your Furnace Winter Ready

A well heated, cozy home is what makes the day better when the winter comes in full fledged. So, it…See More
11 hours ago
Tauran Ivall replied to Tauran Ivall's discussion Energy Efficient Entry Door options out there?
"Thanks Graham, There is a distributor in Portland for them. Thanks for the link to the blog.  "
13 hours ago
Bob Blanchette replied to Rod Fox's discussion Utility Meter Accuracy
"The use of CT's screams commercial service, most likely over 200A. 200A and lower uses simply…"
13 hours ago
Dennis Heidner replied to Rod Fox's discussion Utility Meter Accuracy
"It's not just the CT's that you need to worry about.   The CT will pick up the…"
18 hours ago

© 2015   Created by Lawrence Berkeley National Laboratory.   Powered by

Badges  |  Report an Issue  |  Terms of Service