Can anyone share their experience with air sampling of low pressure 2 part foam in residential homes? I'm about 20 hours into reading endless amounts of information relating to the hazards and need help  Anybody had any experience with OSHA or PELS of typical retrofits?

Views: 339

Reply to This

Replies to This Discussion

Cory, we have tried badges to detect airborne isocyanates.  The ones we tried were not sufficiently sensitive to detect the components in the low pressure foam we were using.

 

We also have talked with our foam manufacturer and with our respirator cartridge supplier.  We concluded that the best way to minimize the risks of long term exposure is to use positive pressure, outdoor supplied air respirators rather than the dual cartridge respirators.  Also, good engineering controls (lots of ventilation) should be used during the foam application.

 

Homeowners definitely need to be out of the house during application and for the manufacturer's recommended period afterwards.  We also recommend that pets be out of the house.  Installers need to be protected from exposure during this period as well.

Thanks Jon, we do all of the above with the exception of the homeownerns leaving. They are denied access to where the foam is being applied and we ventilate.

 

 

As a manufacturer of low pressure SPF, Fomo has done multiple air monitoring studies.  Our Product Stewardship Guidelines outline a typical air monitoring study done in Connecticut. I have tried to attach this, but it can also be found at www.fomo.com.  You can see on page 9 that the concentrations detected were well below OSHA limits.  It's great that you are ventilating and wearing the proper PPE, however, we would agree with Jon that the occupants should vacate during the work and with Handi-Foam SPF for one hour after you have stopped spraying, this typically gives you enough time to clean-up and the homeowner can be back home. 

Attachments:

InsulSmart is a two-part aminoplast interior foam insulation offered by cfiFOAM, Inc. based in Knoxville, TN. InsulSmart - when tested per ASTM D-5116 @ "full chamber"-  showed low emissions rapidly declining from 24.6 ppb @ 7-days, to 6.5 ppb @ 14-days,  to 0.8 ppb @ 21-days, and to less than 0.8 ppb @ 28-days, which is pretty close to zero emissions. The product's low emissions reflect 1) processing to remove virtually all free-formaldehyde prior to packaging; 2) sophisticated cross-linking chemistry that reduces formaldehyde emissions to levels below ambient in many instances.

A report of ASTM D-5116 is attached along with a summary of various federal agency's guidelines. For product information and to view a short video clip, go to www.cfifoam.com.

Attachments:

RSS

Videos

  • Add Videos
  • View All

Latest Activity

Barbara Smith posted videos
53 minutes ago
CharlieK posted a discussion

Eco-Cottage Program Applauded By Housing Groups, Suppliers & Lenders

AmeriSus a leading player in the eco-kit home business kicked off a new program on MLK-day which…See More
4 hours ago
Diane Chojnowski posted a discussion

Call for Nominations: Tony Woods Award and Building Performance Hall of Fame

The Building Performance Institute, Inc. (BPI) is seeking nominations for the 2017 Tony Woods Award…See More
5 hours ago
Diane Chojnowski added a discussion to the group 1000 Home Challenge
Thumbnail

January Webinar: Intro to the 1000 Home Challenge

The January Intro to the 1000 Home Challenge webinar will be  Friday, Jan 20 at 10-11:30 AM eastern…See More
5 hours ago
Diane Chojnowski's event was featured
Thumbnail

Introduction to the 1000 Home Challenge Webinar at Eastern Time

January 20, 2017 from 10am to 11:30am
The January Intro to the 1000 Home Challenge webinar will be  Friday, Jan 20 at 10-11:30 AM eastern…See More
5 hours ago
Diane Chojnowski posted an event
Thumbnail

Introduction to the 1000 Home Challenge Webinar at Eastern Time

January 20, 2017 from 10am to 11:30am
The January Intro to the 1000 Home Challenge webinar will be  Friday, Jan 20 at 10-11:30 AM eastern…See More
5 hours ago
Barbara Smith's video was featured

NY State Weatherization Story

The Weatherization Assistance Program (WAP) is an energy efficiency and conservation program administered by the New York State Homes and Community Renewal (...
6 hours ago
Quinn Korzeniecki added a discussion to the group Building Performance Institute (BPI)
Thumbnail

Call for Nominations: Tony Woods Award and Building Performance Hall of Fame

The Building Performance Institute, Inc. (BPI) is seeking nominations for the 2017 Tony Woods Award…See More
7 hours ago

Home Energy Pros

Welcome to Home Energy Pros – the unique digital community by and for those who work in the home energy performance arena.

Home Energy Pros was founded by the developers of Home Energy Saver Pro (supported by the U.S. Department of Energy) and brought to you in partnership with Home Energy magazine.  Home Energy Pros is sponsored by the Better Buildings Residential Network. Please honor our Guidelines

© 2017   Created by Lawrence Berkeley National Laboratory.   Powered by

Badges  |  Report an Issue  |  Terms of Service