Can anyone share their experience with air sampling of low pressure 2 part foam in residential homes? I'm about 20 hours into reading endless amounts of information relating to the hazards and need help  Anybody had any experience with OSHA or PELS of typical retrofits?

Views: 294

Reply to This

Replies to This Discussion

Cory, we have tried badges to detect airborne isocyanates.  The ones we tried were not sufficiently sensitive to detect the components in the low pressure foam we were using.

 

We also have talked with our foam manufacturer and with our respirator cartridge supplier.  We concluded that the best way to minimize the risks of long term exposure is to use positive pressure, outdoor supplied air respirators rather than the dual cartridge respirators.  Also, good engineering controls (lots of ventilation) should be used during the foam application.

 

Homeowners definitely need to be out of the house during application and for the manufacturer's recommended period afterwards.  We also recommend that pets be out of the house.  Installers need to be protected from exposure during this period as well.

Thanks Jon, we do all of the above with the exception of the homeownerns leaving. They are denied access to where the foam is being applied and we ventilate.

 

 

As a manufacturer of low pressure SPF, Fomo has done multiple air monitoring studies.  Our Product Stewardship Guidelines outline a typical air monitoring study done in Connecticut. I have tried to attach this, but it can also be found at www.fomo.com.  You can see on page 9 that the concentrations detected were well below OSHA limits.  It's great that you are ventilating and wearing the proper PPE, however, we would agree with Jon that the occupants should vacate during the work and with Handi-Foam SPF for one hour after you have stopped spraying, this typically gives you enough time to clean-up and the homeowner can be back home. 

Attachments:

InsulSmart is a two-part aminoplast interior foam insulation offered by cfiFOAM, Inc. based in Knoxville, TN. InsulSmart - when tested per ASTM D-5116 @ "full chamber"-  showed low emissions rapidly declining from 24.6 ppb @ 7-days, to 6.5 ppb @ 14-days,  to 0.8 ppb @ 21-days, and to less than 0.8 ppb @ 28-days, which is pretty close to zero emissions. The product's low emissions reflect 1) processing to remove virtually all free-formaldehyde prior to packaging; 2) sophisticated cross-linking chemistry that reduces formaldehyde emissions to levels below ambient in many instances.

A report of ASTM D-5116 is attached along with a summary of various federal agency's guidelines. For product information and to view a short video clip, go to www.cfifoam.com.

Attachments:

RSS

Home Energy Pros

Home Energy Pros was founded by the developers of Home Energy Saver Pro (sponsored by the U.S. Department of Energy,) and brought to you in partnership with Home Energy magazine.

Latest Activity

Mark posted events
9 minutes ago
Shashank Kirloskar is now a member of Home Energy Pros
12 minutes ago
Everblue replied to Jennifer Luitwieler's discussion Google+//Will it SAVE THE WORLD? in the group Social Media and Energy Efficiency
"haha I totally understand! This has been on my radar for the past 6 months, and I get filled with…"
17 minutes ago
Don Fitchett posted a video

What is Thermography (thermal imaging)

This video "What is Thermography" (What is Thermal Imaging) is a video lecture is an excerpt from http://bin95.com/IR Online thermography training. The main ...
19 minutes ago
Corbett Lunsford posted videos
19 minutes ago
Everblue posted a blog post
20 minutes ago
Diane Chojnowski replied to Hal Skinner's discussion Sorry, couldnt resist
"Funny!"
26 minutes ago
Bob Blanchette replied to Hal Skinner's discussion Any success getting landlords to energy upgrade a single family rental unit?
"The landlords don't want the improvements done even if they don't have to pay for it?…"
23 hours ago

© 2014   Created by Lawrence Berkeley National Laboratory.

Badges  |  Report an Issue  |  Terms of Service